soory read a previous post which implied the length was unknown
i think given what you have mentioned 15KW would be a reasonablly conservative guess at max load (allows for the shower on one socket fully loaded and a couple of other bits on top).
so 15KW at 15m
you could get away with 10mm XPLE SWA but i would advise 16mm PVC or XPLE SWA (XPLE running at its max rating gets bloody hot so you have to be carefull about terminations)
i advise use of 3 core SWA to keep the earth fault loop impedance low.
at the house end i think running this through your existing CU is a bad idea. somthing like http://www.tlc-direct.co.uk/Products/WY108M.html (with a 60A fuse fitted) seems like a good bet. It will need to be henleyed into the tails which requires pulling the service fuse not something that we would reccomend to most diyers (thought there are deffinately diyers here who have done it).
at the outbuilding end a metalclad CU should be used to allow direct termination of the SWA. This should have some form of rcd protection. (either a full RCD box a split load or a non-rcd box with RCBOs)
i think given what you have mentioned 15KW would be a reasonablly conservative guess at max load (allows for the shower on one socket fully loaded and a couple of other bits on top).
so 15KW at 15m
you could get away with 10mm XPLE SWA but i would advise 16mm PVC or XPLE SWA (XPLE running at its max rating gets bloody hot so you have to be carefull about terminations)
i advise use of 3 core SWA to keep the earth fault loop impedance low.
at the house end i think running this through your existing CU is a bad idea. somthing like http://www.tlc-direct.co.uk/Products/WY108M.html (with a 60A fuse fitted) seems like a good bet. It will need to be henleyed into the tails which requires pulling the service fuse not something that we would reccomend to most diyers (thought there are deffinately diyers here who have done it).
at the outbuilding end a metalclad CU should be used to allow direct termination of the SWA. This should have some form of rcd protection. (either a full RCD box a split load or a non-rcd box with RCBOs)