no the other shower will come of the cu down stairs.can you only have one shower of a cu?
Err - can you multiply the current demand of a shower by 2?jbonding said:no the other shower will come of the cu down stairs.can you only have one shower of a cu?
That's very easy to say.jbonding said:both showers wont be on at the same time.
ban-all-sheds said:That's 29kW - he needs to have the electricity supplier run in a new and completely separate supply....
Has he got cable with 25mm² conductors, or something which measures 25mm across?jbonding said:he got 25mm cable of site can he use that.
jbonding - plug makes a point here which is literally of life and death importance.plugwash said:i dunno if the planned route is completely inside the permitted routes for unprotected cables so steel wire armoured may still be a more sensible choice.
2 x 10+ kW showers = 20+kWFWL_Engineer said:ban-all-sheds said:That's 29kW - he needs to have the electricity supplier run in a new and completely separate supply....
How on Earth do you arrive at 29kW from the comment "Two showers, five sockets and a couple of lights"
OK - but that wasn't obvious..jbonding said:the six showers was sarcasm,
You asked a question with none of the information needed to answer it - it was impossibly vague.ban all sheds if youve got nothing but scare tactics dont bother commenting,
What on earth does that mean? Ignoring the fact that you have not said "no live power involved", it's a meaningless concept, unless you're trying to say that what your friend plans to do is to install the cable, and the CU in the loft, and the circuits and accessories and appliances in the loft, but never connect it, or have it connected, to the supply. Which I doubt.i know electric kills, if you go back through the posts you see no live power involved.
You tell me - 2 showers on together is 80-90A. What is the size of your friend's service fuse? What else would he like to have on at the same time?b.a.s said ( being surprised when told that even 2 of them would be a struggle and solving that by simply deciding that they would never be used together,) is it just a struggle or possible?
Yes, you are, and you're getting advice, even if you seem not to like all of it. But you can't get useful advice without providing useful input, and the words "stone" and "blood" come to mind there.b.a.s said (but I just felt that jbonding needed a wake-up call to shock him out of his vagueness - he didn't seem to think that any of this was at all significant ) im on a forum asking for advise about electrics (HELLO)
There's more to Part P than "getting it checked when it's done". Doing that will not meet the requirements of Part P of the Building Regulations and leaving it until then will be too late to meet the requirements of Part P of the Building Regulations....PS hes aware of part P and hes getting it checked when its done.