Okay, so i'm putting in a new circuit (single cable, not ring!) to the old WC at bottom of garden in order to power a ceramics kiln i have.
14M indoor cabling, 16m outdoor.
Kiln is 3.75 KW = 16.3A
So if i do a Voltage drop calc based on 2.5mm cable:
30M * 16.3A = 8.2V : Drop = 3.62%
Question is, is it okay to do one calc for the indoor cable and another for the outdoor cable ? if i split the 2.5mm indoor cable & 4mm outdoor SWA :
Drop = 2.76%
... which means I have another 7 Amps to spare and could install a light !!??
Or even (being greedy now) .. is there anything against me installing a 3 pin socket to supply <= 5 amps ? On the one hand i feel like a cheat with such a plan, it doesn't seem right to fiddle things so.... but theoreticaly i can't fault it !?!?
... lastly (now being very greedy with questions !) ... should i worry about adding in calculations such as corrections for where my indoor cabling is in a conduit alongside other cables (i.e wall chases) , or where it squeezes through a 16mm hole i drilled for it to get through a RSG (for all of 5-10 mm)??
.. or are you going to tell me to fit 4mm cable all the way through and stop being a Scrooge ?
Sorry to ask so many questions in one posting .... but hey, if you don't ask, the electrician will only tell you for £50 when he comes to 'approve' your installation, then another £50 when he comes again after you fixed it all (nothing against electricians .... i'm just skint !!)
Many many thanks
Simon
14M indoor cabling, 16m outdoor.
Kiln is 3.75 KW = 16.3A
So if i do a Voltage drop calc based on 2.5mm cable:
30M * 16.3A = 8.2V : Drop = 3.62%
Question is, is it okay to do one calc for the indoor cable and another for the outdoor cable ? if i split the 2.5mm indoor cable & 4mm outdoor SWA :
Drop = 2.76%
... which means I have another 7 Amps to spare and could install a light !!??
Or even (being greedy now) .. is there anything against me installing a 3 pin socket to supply <= 5 amps ? On the one hand i feel like a cheat with such a plan, it doesn't seem right to fiddle things so.... but theoreticaly i can't fault it !?!?
... lastly (now being very greedy with questions !) ... should i worry about adding in calculations such as corrections for where my indoor cabling is in a conduit alongside other cables (i.e wall chases) , or where it squeezes through a 16mm hole i drilled for it to get through a RSG (for all of 5-10 mm)??
.. or are you going to tell me to fit 4mm cable all the way through and stop being a Scrooge ?
Sorry to ask so many questions in one posting .... but hey, if you don't ask, the electrician will only tell you for £50 when he comes to 'approve' your installation, then another £50 when he comes again after you fixed it all (nothing against electricians .... i'm just skint !!)
Many many thanks
Simon