I've just tried playing browsers.I don't know; I'm not that tech-savvy.
Only a slight one. Previously, I saw only placeholders in both the posted message and also in the Reply Box when I "quoted" the post. This time, although I see only the placeholders in your post, as I type this in the Reply Box (quoting your message) I am looking at the actual image for your first image, but only a placeholder for the second one.
Any differences?
As previously stated it is likely that the existing cable is safe, which can be proven by a few measurements and calculation.
It still won't comply with BS7671 (wiring regulations) for the reasons above.
Agreed, electrically speaking. However, some people would undoubtedly be concerned about 'deliberately'/'knowingly' having something which is not compliant with BS7671.Davey - IMO flameport's sentence above is the most useful one on all of this thread, in relation to your original question at least.
Get one with a light in it, then you've got a lighting circuit.
If it turns out that is 1.5mm², it would probably even be compliant with regs (despite the fact that some people might be {unnecessarily} 'worried' by the fact that it's not one of the arrangements shown in the 'informative examples' in an Appendix to the regs!) as well as being electrically fine.In hindsight the feed cable may even be 1.5mm - I only know it's thinner than 2.5mm.
Probably ???If it turns out that is 1.5mm², it would probably even be compliant with regs
I think that would be stretching the realms of - what? quibblingforthesakeofquibblingness - beyond all reasonable bounds.(despite the fact that some people might be {unnecessarily} 'worried' by the fact that it's not one of the arrangements shown in the 'informative examples' in an Appendix to the regs!)
Exactly.as well as being electrically fine.
Yes, probably - i.e. given that we would be relying on downstream overload protection, it would be compliant provided that the circuit's OPD (probably a B32) provides satisfactory fault protection for a 1.5mm² cable (which it probably would).Probably ???
Whatever you call it, we have seen it. The diagrams in Appendix 15 do not show a socket being fed directly from a ring final or a radial with 1.5mm² cable. As I said, that seems to worry some people. Indeed, I wouldn't bet on the suggestion that no electrician undertaking an EICR would flag it up as a 'non-compliance'!I think that would be stretching the realms of - what? quibblingforthesakeofquibblingness - beyond all reasonable bounds.
I'm not sure what part of my attitude you feel has been "ultra-conservative". What I personally feel, what I think about a particular regulation and what I would happily do in my own home are one thing, but, when it comes to informing/advising an OP, I think it's only right that the OP should be made fully aware of what the regulation appears "to actually say", whatever you, I and others think/feel about it.In view of the fact that you sometimes argue with Bas and say you don't think this or that regulation means what it says, I don't understand your ultra-conservative attitude in this thread.
Yet you say that's ok without qualification when I advise people to check oven circuits because of that.Yes, probably - i.e. given that we would be relying on downstream overload protection, it would be compliant provided that the circuit's OPD (probably a B32) provides satisfactory fault protection for a 1.5mm² cable (which it probably would).
The only regulation it contravenes is the ridiculous Table 52.3.I'm not sure what part of my attitude you feel has been "ultra-conservative". What I personally feel, what I think about a particular regulation and what I would happily do in my own home are one thing, but, when it comes to informing/advising an OP, I think it's only write that the OP should be made fully aware of what the regulation appears "to actually say", whatever you, I and others think/feel about it.
If I have ever said that, I'm surprised, because one really can't say it 'without qualification' - since it depends upon the EFLI as measured in that part of the circuit. In any event, I was merely echoing what Risteard and flameport had said back on page 1 (that confirmation of adequate fault protection was necessary to establish compliance); had I contradicted that (which I wouldn't want to, anyway), I would probably have confused the OP even more!Yet you say that's ok without qualification when I advise people to check oven circuits because of that.
Yep, we are agreed about that (provided that fault protection is OK).The only regulation it contravenes is the ridiculous Table 52.3.
Indeed.Had the installer used 1mm² (or even 0.75mm²) flex. it wouldn't even do that. It might not then be big enough for the fire but that's another issue.
If it turns out that is 1.5mm², it would probably even be compliant with regs
(despite the fact that some people might be {unnecessarily} 'worried' by the fact that it's not one of the arrangements shown in the 'informative examples' in an Appendix to the regs!) as well as being electrically fine.