I'm not totally sure what everyone is saying here. If the OP is suggesting inserting a 13A FCU fairly close to where the spur joins the ring (and before any sockets/loads), then he can (within reason) run as many sockets as he wishes from that FCU, and even in 1.5mm² cable (after the FCU) if he so wishes. Indeed, that's explicitly one of the arrangements shown in Appendix 15 of the regs.I'm afraid that doesn't help. An FCU that could take a 13 amp fuse is really no different from a single socket with a 13 amp fused plug in it.littleleaks said:Is it better when taking a spur to use a fused box? ie cut the cable which is currently a spur install a fused box and then run the new spur from that?
What he cannot do is add a FCU after any load/socket on the spur.
Kind Regards, John.