you need to check what fall, might get away with a 1:150 fall depending on the size of the pipe (a drawing should tell you). Some falls have to be 1:80 or 1:40 though which would be a problem.
Minimum fall for a w/c soil pipe is 18mm/m which equates to 1:55; maximum gradients on baths/wash basins etc vary but all are also 18mm/m up to 90mm/m
Yes, you should really have an AAV which you can hide but it must be accessible and 300mm above flood height - its' instead of sticking a soil vent pipe thru your roof or, as in ur case, 6m from the external svp.
Mostly correct; you can only fit an AAAV if you have another open stack on the system which will cater for positive ass well as negative pressures which an AAAV can’t do, otherwise you’d get all those nasty smells. Regarding the valve mounting height; it must obviously be fitted above the highest waste flood point (usually the top of the wash basin) but the although a reference of 300mm above the flood height is regularly mentioned, as far as I’m aware there is no such requirement, it just has to be above the highest spillover point.
You should also consider that if teeing into the 110mm w/c line with shower/sink waste & depending on layout, your other appliances will probably need venting or fitted with anti-siphon traps.
Other option might be a macirator, like a poo chopper which pumps the crap thru a smaller pipe...nice.
As I said, to be avoided at all costs unless there is no other option. Not so much of a problem if your responsible about what you put down there & don’t have any kids but I’ll leave you to imaging what a pleasant job clearing a blockage in one would be!
So would the fall height be measured 'sub-floor' or from the toilet's output (e.g. 6" above the floor)?
The fall is measured over the length of the pipe; i.e. the pipe must fall 18mm for each 1 metre length; the vertical drop from the w/c is irrelevant.
Also, with the AAV, does this need to run straight above the toilet? I ask because the WC is below the lowest point of the pitched roof - if it did need to go straight above the WC then it'd need to go through the roof anyway. If not, could the vent pipe be run diagonally up the pitched roof and vent at a higher point?
The vent stack can go at any angle you want, its sole purpose is to let in air. The AAAV must also be fitted above the highest flood line, accessible & the actual bit of pipe it’s fitted to must be vertical or it won’t vent properly.
Download the PDF "Design Criteria";
http://www.hunterplastics.co.uk/content/1/94/soil---waste-support.html
I've posted this link so many times now, I’m worried folks might think I’ve got some connection
For the record, I haven’t it's just I think it’s a really useful little guide which is easy to understand & includes BR requirements.