the only other slight tell tale sign would be the lack of CPC on lighting circuits which happended late 50's and into the 60's.
The IEE Wiring Regs. didn't require an earth on all lighting circuits until the 14th edition in 1966. However, earths
were required before then in certain circumstances, such as for metal light switches, fluorescent lights, metal wall lighting fixtures within reach, etc.
As some other general guides, PVC-sheathed cables started to appear from the mid-1950's, but as you would expect the changeover was gradual and rubber-sheathed were still commonly being installed into the 1960's for general household wiring.
If you have 3-core (or 3-core plus earth) running to 2-way switches, the core colors can be another clue: Red/white/blue cores indicate that the cable dates to the 1963/64 period or earlier, since that's when the colors were changed to red/yellow/blue.
Metric cable started to come into use around 1970, so an installation with all metric-sized cables will be no earlier than that, e.g. ring circuits with metric cable will be solid 2.5 sq. mm conductors which have a bare copper appearance, whereas the older Imperial cable was stranded 7/.029 with tinned copper strands having a silver appearance (however aluminum conductors were used for a short time in the 1960's/70's which will, obviously, appear silver as well).
The recent introduction of "harmonized" European colors for cables about 5 years ago is already well known. Flexes adopted brown, blue & green/yellow around 1970 in place of red, black & green, so any which form part of the fixed wiring (e.g. between a fused spur unit and a fixed appliance) can give another clue.
Bonding and main earthing conductors (to pipework, external earth rod, etc.) are another indicator, assuming the original installation was done to the current IEE Regs. of the time. Prior to 1966 bonding cables were generally black (if not bare); from the 14th edition they became green, then later changed to green/yellow (the exact date escapes me - early 1980's if I recall correctly).
Earths at sockets and light switches (where used) also changed: Up until the mid-1970's they were generally left bare, then the Regs. specified sleeving in green, changed to green/yellow at the same time as the main bonding & earthing made the similar change.
Obviously all of that is a
general guide, since there was always something of an overlap period where, for example, metric cable was introduced but homes were still being wired with old stocks of Imperial cable.