Softus said:
Where is this responsibility defined? Is it, like a great many things, only in your head?
In the law.
They buy a boiler, they want a working boiler.
If the new boiler is incompatible with the existing system ( which may have been installed for a coal-fired, open-vented, back boiler, or which may be full of black sludge) then you need to tell them, you need to modify the system to suit the new boiler and/or you need to secure a signed disclaimer that explains the problem and that they have declined to have it rectified.
You/We being competent tradesmen are expected to know these things and to advise the customer accordingly.
The customer is ignorant of these things, That is why he has employed a competent tradesman.
megawatt said:
The installer cannot be held responsible for the entire installation simply when a boiler is changed as there are many aspects of it which are unknown ... Quality of hidden plumbing etc.
You are not responsible if, the day after you leave the property post boiler comissioning, the house is flooded due to a previously badly fitted compression fitting popping off ... Though I can understand why the customer may think that you are
The installer is held responsible.
Working pressure of an open-vented system, 0.5 bar.
Working pressure of a sealed system 2.0 bar, say.
So, knowing that, you'd pressure test the existing system, to 1.5x or 2x the working pressure (certainly more than the PRV setting), before fitting a new sealed system boiler.
You didn't pressure test it and a compression joint popped off?
The fitting was adequate for 0.5 bar. You changed the system, it is your responsibility. It is negligence. The liability for negligence is 15 years, or 5 years from the date to discocery of the defect.
If it were my house, I'd sue you.
You'd lose.
The sealed system keeps losing pressure? Your problem (unless a detailed disclaimer is obtained), the existing open-vented system was adequate.