Did you have the same problem with the old radiators ?
Radiators distribute the heat, the room utilises and dissipates that heat. The higher the heat loss in the room the quicker the room will utilise that heat.
Pipework has a limit for the maximum amount of kWs it can carry. An 8mm pipe with a flow rate of 0.9 metres per second can carry approx 2250watts (or 2.25kW). Compare that to a 15mm pipe which at the same flow rate can carry up to 8.25kW or a 22mm pipe that can carry 18kW. What you have done is upgraded the radiators, but they still distribute the same amount of heat but it is dissipated amongst more panels. Whereas before you had 2.25kW distributed amongst say 4 panels, now you have 2,25kW distributed amongst 8 panels (assuming you upsized 4 single panel rads to double panel). Not only will the radiators heat more slowly, they will dissipate a lot less heat.
Bigger radiators have a larger surface area and with the same heat input will naturally run at a "lower temp" but they are still dissipating the same amount of heat. More radiators also increase the pressure (i.e. resistance) in the system so the pump must work harder to compensate.
Increasing the pump speed will help but it will only take you so far. The faster the pump runs the more corrosion it causes within the system due to friction against the pipework.
The heating engineer should have done a heat loss calculation to identify how much heat you are losing in the property, the heat output of all the radiators, and then calculate whether the current pipework would be able to carry sufficient kWs to supply the rads, and if not, then appropriately up size the pipe where necessary.
If increasing pipesize is too much you can always increase insulation thereby reducing your heating needs.