Radiator output approx 34kw
So you need a 32kW boiler which, assuming it includes 2kW for the HW cylinder, means a heating load of 30kW. Your rads add up to 34kW, but that's when running with a 50°C ΔT. If the ΔT is lower the rad output will be lower. It's not a linear relationship. Reducing ΔT by 20% to 40C will reduce the output by 25%.
A quick explanation: ΔT is the difference between the mean water temperature and the room temperature. Rad outputs are measured with a flow temp of 75C, return of 65C and room temp of 20C. The mean water temp is therefore 70C and ΔT is 70-20 = 50C.
1. Most are around 1/4 to a half turn
2 12 deg C to 15 deg c at the moment
3.Flow 71 deg Return 45 deg c
1 and 2 are good, but why is there such a large drop at the boiler? I would have expected the return to be about 55-56C. Is there a large run of pipe from the boiler to the first rad?
What are you using to measuring the temperatures?