You have to work from index rad all the way back to the boiler.
You seem to have taken only one radiator into account. If you look at Fig 3 and the accompanying table in the second link, you will see that all rads have to be taken into account. This is because, as you get nearer the boiler, there is more water flowing through the main pipes, so the resistance increases.
You say the heat load is 30kW. Is this a guess or have you calculated the loss?
The Vokera has a built-in pump and is designed to work with a 20C differential. This needs to be taken into account when sizing the radiators and calculating the index circuit resistance.