Over 150sqm you need to have two zones with separate time and temperature controls.
I thought you said elsewhere that the requirement for two zones when over 150 sq m was dropped a couple of years ago?
I hope I didn't say that as it's wrong.
Current requirements as set out in the
Domestic Building Services Compliance Guide 2010 are quite clear:
Up to 150sqm: 2 zones with separate temperature controls
Over 150sqm: 2 zones with separate time and temperature controls
The only exception is for single storey dwellings where the living area is over 70% of the floor area. In this case only one zone is required. This could cover anything from a bedsit to a large open plan loft in a converted warehouse.
While nothing has really changed for
over 150sqm cases - it will require a S Plan Plus system, ie zone valves on each heating zone -
under 150sqm requirements have changed from those in the 2006 Guide.
2006: Two zones - room stat in one zone, TRV elsewhere (option 2 in my last post)
2010: Two zones - room stat in main area of each zone, TRVs elsewhere. (i.e only 2006 option 3 in my last post)
This effectively means that you have to have two zone valves for both over and under 150sqm. The only difference is that under 150sqm you need just a single timer and two thermostats; over 150sqm you need two timers and two thermostats.