Tony:
Even that Gledhill diagram is wrong!
It shows a TRV on the heat dump radiator above the multifuel stove. No TRV should be fitted ( unless it was a special reverse action TRV ).
Yes, I can see that would be a bad idea.
No as your store and hence your rads will only ever get as hot as the heat input from the heat source
<snip>There are valid reasons to use a blending valve where it is but that would be as a secondary safety device for limiting/safety reasons
No valid reason for the pump position if it is in fact part of the heating system
Do you have underfloor heating or a wood burner?
Matt
Woodburner and I think the thermal store vents @ 80 - 90 (actually the solar vents when the bottom gets to 80 and I think the top is 85 or 90), so I can see the need for something.
Well, the data sheet I read said that your blending valve is suitable for heating. Your pump should be be on the system side of the valve, on the flow leg, not between the coil and the valve. This will alleviate any pressure difference problems.
You need to have the pump in the right place on the system. Colder return leg enters the bottom of the valve. A check valve might be held shut if you fit one with your pump in it's current position.
Thanks, do you have a link to the data sheet and / or docs on position of the pump. I need to go back to the installer and get it remedied.
You have all been a great help. I'll step over to the software section to see if I can return the favour somehow.
I have other questions, but will start a new thread:
- air distribution system (living room too hot with stove, kitchen too cold, thermal store on wood only not able to heat kitchen enough).
- Is my thermal store big enough?
My take away at the moment is:
- Pump required (otherwise no delivery to the rads)
- valve required if thermal store much hotter than we want the rads
- Pump position - consensus is on the other system side (which I assume is rad side), but 2 views, one of the flow and the other on the return.