I did stop when you originally pointed out they were combi boilers, I just had it in my head I had 6 screws but I really have 4.
I tried googling "replace system boiler proving pin", "replace system boiler diaphragm", "baxi system boiler". I found this video
. I then came across this video about air in the boiler (time 3:45 into it)
. This might come in handy if I end up with air in it at the end (should I get air in?)
I am attaching photos of my boiler (last one is the back of the unit with the diaphragm). The big bolt on rubber was something I put in to prop up the pump as it was making an annoying humming noise which disappeared if I held the pump).
Can you please explain the sequence required to safely access the diaphragm (and small hole behind it) and reassemble? As far as I can tell the process is now
1) turn off the 2 valves (with the black handles) under the boiler, then connect a tube to the drain off point nipple
2) put the other end of the tube into a bucket
3) open the drain off point valve and wait for the water to go into the bucket until the pressure gauge reads zero or the water stops
4) put rags around the proving pin housing and PCB
5) undo the 4 screws on the proving pin housing
6) carefully open the cover (spring inside)
7) clean the parts with descaler
8) clean the hole the proving pin slides in
9) check the rubber diaphragm (order new one if necessary) and clean the small hole behind the diaphragm
10) reassemble parts
11) close the drain off point valve
12) open the 2 valves under the boiler
13) repressurise the system
14) turn the boiler on, demand some heat, if i hear air in the boiler undo the drain off valve for 30 seconds to let air out (should hear it spluttering with the water?) then tighten the drain off valve
15) remove tubing
16) consider adding more inhibitor (last time was sentinel X100)
Thanks
Darren