What was the voltage?At that time ELI for a 32A ring was 1.44Ω and the extended ring was showing 1.50Ω was that enough (pre-2008) to worry about anyway?
That's surely not relevant, is it? Prior to 2015 (Amd3), the maximum Zs was calculated on the basis of the nominal 230V supply voltage (hence 1.44Ω for a B32), and since then has effectively been calculated on the basis of 218.5 supply voltage (230V x 0.95). At no time that I'm aware of has it been permissible to determine maximum Zs on the basis of what the actual supply voltage happened to be at some point in time (hence 1.37Ω for a B32).What was the voltage?
Probably not.... or am I perhaps missing the point of your question?
Fair enough, and I agree - but as you acknowledge, reg-wise it has never been permissible to have a Zs which would not be 'alright' at 230V (now 218.5V), even if it was 'alright' with the supply voltage as it was when measured.Probably not. I was just implying, with relation to Eric's figures, that 1.50Ω would be alright if the actual voltage was 240V or above although not compliant with the printed maximum figures for a nominal 230V (prior to Cmin.).
Maybe, but that might suggest a degree of honesty! It would arguably be even more of a "remarkable coincidence" had the Zs been recorded as exactly 1.44Ω !A remarkable coincidence that it was exactly 1.50Ω, though.
I perhaps should have added that if one is being 'pragmatic', rather than strictly complying with regs, then it's worth remembering that (contrary to what some people seem to imply) nothing dreadful suddenly happens if the Zs of a circuit slightly exceeds the "printed maximum". If the Zs does slightly exceed that maximum, then the only consequence would be that the 'worst case' disconnection time would slightly exceed the (essentially arbitrary) 'required value'.I was just implying, with relation to Eric's figures, that 1.50Ω would be alright if the actual voltage was 240V or above although not compliant with the printed maximum figures for a nominal 230V (prior to Cmin.).
the only consequence would be that the 'worst case' disconnection time would slightly exceed the (essentially arbitrary) 'required value'.
I'm not convinced that there is not a lot of difference between "not quite arbitrary" and "essentially arbitrary"