It is, for Type B, that they trip (instantaneously) at between 3 and 5 times their In. We calculate the worst case at 5x but I do not know what they actually are - maybe 4x. .... Similar, although you don't seem to know about the 3 to 5 times requirement.
You seem to be assuming an answer to the question I'm asking, and to which I don't know the answer for certain.
Yes, we talk about a Type B MCB tripping magnetically between 3I
n and 5In, but what does the Standard actually say? If it really does say that, in the 'worst case' scenario, the device has to be guaranteed to trip magnetically at
exactly 5I
n, but not necessarily at a current fractionally below that, then this would mean (assuming symmetrical measurement errors) that 50% of cases in which measurement + calculation indicated a fault current of
exactly 5I
n would actually be 'unsafe'.
Maybe that is the case, but, if so, it would seem rather unsatisfactory. I'm therefore speculating that when we say that the MCB has to trip at 5In, the Standard might actually require that it trips at 5I
n - x%, to make allowance for measurement error. If it doesn't, then BS7671 really ought to drop its 'maximum Zs' figures a bit to 'keep things safe' even when loop impedance measurement was done by a slightly 'under-reading' meter.
Returning to your initial comments, I wonder if, in practice, even if there is a requirement for magnetic tripping at "3I
n-5I
n" that, in practice, virtually all of them trip at a current closer to 3I
n than 5I
n? Unfortunately, very few of us have the ability to determine that by experimentation ourselves!
Kind Regards, John