Wrong again.... The main reason for the size is the unvented cylinder, not the heat loss from the house...
The main reason is that every penny counts and they don't give a toss what problems the buyer will have; profit is the only motivator.
Wrong again.... The main reason for the size is the unvented cylinder, not the heat loss from the house...
I have seen four bed detached houses with two bathrooms which only have a 15kW boiler. The main reason for the size is the unvented cylinder, not the heat loss from the house. The 3-bed semis had 12kW boilers.
Bet the customer won't be impressed with the time it will take to run a bath with a combi based on this method....But for replacement boilers in UK houses and flats we should now use "The Whole House Boiler Sizing Method" for boiler sizing.
So with regards to my question on here, this method of boiler sizing is irrelevant as I am getting a combi boiler....
I know; but you are not comparing like for like.A little bigger than the 5 kw you were quoting.
The 5kW was for the heating only of a 3 bed mid-terrace house. While the 12kW and 15kW were for detached or semi-detached houses and included an allowance for the vented HW cylinder.
If you want true comparisons of the heat loss they are:
Mid-terrace - 4.94kW
Semi - 5.93kW
Detached - 6.81kW
But for replacement boilers in UK houses and flats we should now use "The Whole House Boiler Sizing Method" for boiler sizing.
Just did a quick google and this is the 1st one that I found.
http://www.wessexwoodboilers.co.uk/pdfs/359782525_boiler_size.pdf[/QUOTE]
A more user-friendly one can be found at Boiler Size Calculator
I don't know where BenG gets the idea from that boilers have huge modulation ratios. 3 to 1 seems about the norm, though there are exceptions. For example: the Remeha 39C has a 5.5:1 ratio and Geminox make one with a 10:1 ratio.
But even if the boiler has a large modulation ratio, the lowest output will often be higher than that required. And if we take into account the fact that the boiler output is calculated on worst case conditions, so most of the time the boiler will be running well below the calculated output, fitting a boiler which modulates down to 12kW when the calculated is 10kW makes no sense at all. Most of the time the boiler will be putting out 5 or 6kW, which it can only do by running in on/off mode. Modulation wasn't invented so installers did not have to range-rate a boiler!
From working as a RGI; quite a bit different than googling things from your armchair.I don't know where BenG gets the idea from that boilers have huge modulation ratios....
At last, someone who does not have preconceived ideas!I could comfortably heat my house with a 5kW boiler, and it is detached.
I agree; but I was not suggesting a 5kw combi boiler.I dread to think how long a bath would take with a 5kW combi and a shower would be impossible. The old 27kW nominal (19kW output) combi I used to have was just about OK both for shower and bath and very few people would be happy with anything less powerful.
Music to my ears!The modern trend for every more powerful hot water supplies with better insulated houses (plus low flow temperatures, weather compensation, and TRVs) means that combis frequently don't modulate down low enough. A 30kW combi might modulate to 6-8KW but typical heating needs 90% of the time will be less than half that. The 35+kW combis that are now almost the norm modulate to around 10kW which is way higher than most modern houses can use.
I assume you mean BenG and all the other Luddites who have not moved with the times.Just have to deal with it, not the end of the world.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local