Condensing boilers require return temps of below 55C to condense and achieve higher efficiencies. With regard to CH this can be achieved on a 20C temp drop with a flow temp of up to 75C (say 70C to allow a margin). Return temp will then be around 50C. In warmer weather the flow temp (and therefore return temp) can be reduced.
However it's not so simple when heating a hot water store (cylinder) where the object is to bring the store to say 60C within a reasonable time. When the hot store is relatively cold, a flow temp of say 70C will result in very low return temps but as the store approaches 60C the return temp will also approach 60C and the boiler will not be able to condense.
I have an idea for resolving this problem which I would welcome comments on. My suggestion is that instead of having the HW thermostat fixed to the cylinder wall it is fixed to the return pipe from the cylinder coil and then set to switch at say 50C so that the boiler return would never exceed that temp and it would always condense.
The HW circuit would then work for any boiler flow temp down to about 55C. Boiler thermostat can therefore be adjusted over a wide range (80C - 55C) in accordance with external temps (this function could easily be automated with an external sensor). During the summer the boiler thermostat could be left on any setting within the range since return temps would never be above 50C.
The actual HW temp would vary with the flow temp, although I don't think the return stat would allow HW temps to exceed 60C (if so it might be necessary to retain the cylinder mounted stat as well). The result would be slightly higher HW temps in cold weather and vice versa, which would be appropriate to demand. During the summer a higher flow temp will give faster reheat times.
Does anyone think this makes sense, or can much the same be achieved with the HW stat on the cylinder wall?
However it's not so simple when heating a hot water store (cylinder) where the object is to bring the store to say 60C within a reasonable time. When the hot store is relatively cold, a flow temp of say 70C will result in very low return temps but as the store approaches 60C the return temp will also approach 60C and the boiler will not be able to condense.
I have an idea for resolving this problem which I would welcome comments on. My suggestion is that instead of having the HW thermostat fixed to the cylinder wall it is fixed to the return pipe from the cylinder coil and then set to switch at say 50C so that the boiler return would never exceed that temp and it would always condense.
The HW circuit would then work for any boiler flow temp down to about 55C. Boiler thermostat can therefore be adjusted over a wide range (80C - 55C) in accordance with external temps (this function could easily be automated with an external sensor). During the summer the boiler thermostat could be left on any setting within the range since return temps would never be above 50C.
The actual HW temp would vary with the flow temp, although I don't think the return stat would allow HW temps to exceed 60C (if so it might be necessary to retain the cylinder mounted stat as well). The result would be slightly higher HW temps in cold weather and vice versa, which would be appropriate to demand. During the summer a higher flow temp will give faster reheat times.
Does anyone think this makes sense, or can much the same be achieved with the HW stat on the cylinder wall?