Hi people
Just confirming Ive got this right... Most of this work has been done after reading and inwardly digesting the regs but after reading a lot of your posts I'm now beginning to wonder whether I got it right... so much conflicting advice... so if I have made any glaring omissions please let me know!
Property is 4 bedroom with separate garage immediately adjacent to the house (4" between them). Overhead supply, no earth from REC. Existing earth was to steel water pipes entering the house. Existing wiring was rubber insulated 1953 effort!
So heres what I did!
New CU (Not split load) with 100A incomer.
32A RCBO's for following circuits:
Ground Floor Ring - 2.5mm T&E <68m of cable
Upstairs Ring - 2.5mm T&E <68m of cable
Kitchen Ring - 2.5mm T&E < 68m of cable
45A RCBO's for:
Oven Radial - 6.0mm T&E <10m of cable - No socket on Control unit
Hob Radial - 6.0mm T&E <10m of cable - No socket on Control Unit
6A MCB's for:
Downstairs lights I - 1.5mm T&E
Downstairs lights II - 1.5mm T&E
Upstairs lights I - 1.5mm T&E
Upstairs lights II - 1.5mm T&E
40A MCB's for:
Radial to Garage - 6mm T&E - 15m to Garage CU (see later)
Radial to Attic - 6mm T&E - 4m to Attic CU (see later)
Radial to Boiler House - 6mm T&E to Boiler House CU (seelater)
16A MCB for:
3kW Immersion Heater Radial - 2.5mm Y&E - 5m
Garage CU:
Incoming cable runs under upstairs floor in house, through house wall, across 4" gap and through Garage wall in conduit to Garage CU.
Has 40A 30mA RCD with 32A MCB connected to 2.5mm T&E ring around garage and 6A MCB for radial lighting circuit. Ring circuit has 13A FCU's for outside floodlights/bulkhead lights and has spurs to suitable exterior grade sockets in attached greenhouse.
Attic CU:
Incoming cable runs entirely in House to attic to CU. Has 40A 30mA RCD with 16A MCB for 2.5mm T&E Radial circuit for sockets - supplies Heating controls and LPG Boiler and various TV amplifiers and splitters. Also 6A MCB for Attic lighting.
Boiler House CU:
Incoming cable runs entirely in house (Boiler house is attached) to CU. Has 40A 30mA RCD with 32A MCB for 2.5mm Ring circuit for sockets - supplies water softener and Heavy duty Washing machine and Tumble Dryer and 6A MCB for lighting.
Additional items:
Some outside sockets have been taken (as spurs) from Downstairs ring main. Suitable exterior sockets were used (MK models)
Outside flood lights/PIR sensors and Bulk head lights have been fitted as spurs using 13A FCU's from upstairs ring main.
New Earthing rod fitted in Earthing rod pit using 16mm sheathed earth cable to Connector block (heavy duty type service connector type) and from there to CU. Also from Connector block - main equipotential bonding to Incoming water and Gas pipes in 16mm earth cable. All appropriate 'Safety Electrical connection' tags have been used.
Bathroom lights are of the 12 SELV type Halogen downlighters and the Shaver socket is powered by spur from one of the upstairs lighting circuits.
No electric shower - nor will there be one - ever!
Yellow and Green earth sleeving was used throughout installation as was Red 'Line' sleeving used for switch drops.
My questions, stimulated by discussions here, are these:
Although I have had no problems with nuisance tripping should I have used a type C RCBO for the F/F?
Should I have used an RCBO on the house end of the cable to the garage or perhaps a time-delayed RCD? What difference would a time delayed RCD make?
Should the cable to the garage have been 10mm T&E instead of 6mm? Perhaps I will want a Hot tub eventually!
Do you see anything wrong with what I have done?
Any advice you can give is greatly appreciated in advance.
Just confirming Ive got this right... Most of this work has been done after reading and inwardly digesting the regs but after reading a lot of your posts I'm now beginning to wonder whether I got it right... so much conflicting advice... so if I have made any glaring omissions please let me know!
Property is 4 bedroom with separate garage immediately adjacent to the house (4" between them). Overhead supply, no earth from REC. Existing earth was to steel water pipes entering the house. Existing wiring was rubber insulated 1953 effort!
So heres what I did!
New CU (Not split load) with 100A incomer.
32A RCBO's for following circuits:
Ground Floor Ring - 2.5mm T&E <68m of cable
Upstairs Ring - 2.5mm T&E <68m of cable
Kitchen Ring - 2.5mm T&E < 68m of cable
45A RCBO's for:
Oven Radial - 6.0mm T&E <10m of cable - No socket on Control unit
Hob Radial - 6.0mm T&E <10m of cable - No socket on Control Unit
6A MCB's for:
Downstairs lights I - 1.5mm T&E
Downstairs lights II - 1.5mm T&E
Upstairs lights I - 1.5mm T&E
Upstairs lights II - 1.5mm T&E
40A MCB's for:
Radial to Garage - 6mm T&E - 15m to Garage CU (see later)
Radial to Attic - 6mm T&E - 4m to Attic CU (see later)
Radial to Boiler House - 6mm T&E to Boiler House CU (seelater)
16A MCB for:
3kW Immersion Heater Radial - 2.5mm Y&E - 5m
Garage CU:
Incoming cable runs under upstairs floor in house, through house wall, across 4" gap and through Garage wall in conduit to Garage CU.
Has 40A 30mA RCD with 32A MCB connected to 2.5mm T&E ring around garage and 6A MCB for radial lighting circuit. Ring circuit has 13A FCU's for outside floodlights/bulkhead lights and has spurs to suitable exterior grade sockets in attached greenhouse.
Attic CU:
Incoming cable runs entirely in House to attic to CU. Has 40A 30mA RCD with 16A MCB for 2.5mm T&E Radial circuit for sockets - supplies Heating controls and LPG Boiler and various TV amplifiers and splitters. Also 6A MCB for Attic lighting.
Boiler House CU:
Incoming cable runs entirely in house (Boiler house is attached) to CU. Has 40A 30mA RCD with 32A MCB for 2.5mm Ring circuit for sockets - supplies water softener and Heavy duty Washing machine and Tumble Dryer and 6A MCB for lighting.
Additional items:
Some outside sockets have been taken (as spurs) from Downstairs ring main. Suitable exterior sockets were used (MK models)
Outside flood lights/PIR sensors and Bulk head lights have been fitted as spurs using 13A FCU's from upstairs ring main.
New Earthing rod fitted in Earthing rod pit using 16mm sheathed earth cable to Connector block (heavy duty type service connector type) and from there to CU. Also from Connector block - main equipotential bonding to Incoming water and Gas pipes in 16mm earth cable. All appropriate 'Safety Electrical connection' tags have been used.
Bathroom lights are of the 12 SELV type Halogen downlighters and the Shaver socket is powered by spur from one of the upstairs lighting circuits.
No electric shower - nor will there be one - ever!
Yellow and Green earth sleeving was used throughout installation as was Red 'Line' sleeving used for switch drops.
My questions, stimulated by discussions here, are these:
Although I have had no problems with nuisance tripping should I have used a type C RCBO for the F/F?
Should I have used an RCBO on the house end of the cable to the garage or perhaps a time-delayed RCD? What difference would a time delayed RCD make?
Should the cable to the garage have been 10mm T&E instead of 6mm? Perhaps I will want a Hot tub eventually!
Do you see anything wrong with what I have done?
Any advice you can give is greatly appreciated in advance.