Just had a new consumer unit fitted it has 5 MCB and 1 RCD the electrician said it is 17th edition but someone has told me it should have 2 RCDs and the MCB should be split between them who is right.
True, but 314 implies that one should not have all final circuits run off one RCD.There is no specific Reg stating that you can’t fit a consumer unit with only one main RCD
Just had a new consumer unit fitted it has 5 MCB and 1 RCD the electrician said it is 17th edition but someone has told me it should have 2 RCDs and the MCB should be split between them who is right.
should not
Just had a new consumer unit fitted it has 5 MCB and 1 RCD the electrician said it is 17th edition but someone has told me it should have 2 RCDs and the MCB should be split between them who is right.
Can we see a picture of your consumer unit, please?
Yes, that's the usual convention in such documents. However, the 'should' word was mine, the actual word in 314.1 of the regs being 'shall':Rather than must not! Should is classed as advisory not mandatory (if anything can be mandatory in a set of guidelines)should not
It's obviously all a bit vague. In most fiedls I work in, 'shall' is close to the 'must' end of the 'may....should....must' spectrum - although, in the absence of definitions (and particularly given that BS7671 is not mandatory in the first place), there is clearly scope for varying interpretations.314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
... (iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit.....
Just had a new consumer unit fitted it has 5 MCB and 1 RCD the electrician said it is 17th edition but someone has told me it should have 2 RCDs and the MCB should be split between them who is right.
Can we see a picture of your consumer unit, please?
From left to right
RCCB 80A,shower,cooker,sockets,lights,boiler,main switch
In that case you have been diddled and the electrician has lied to you.
To comply with 17th edition, all circuits must be RCD protected. This is required if wiring is concealed less than 50mm from the surface (yours will be).
The two circuits on the right next to the main switch have no RCD protection.
The MCBs should be removed and changed for RCBOs or he needs to install a board that DOES comply. One of these http://www.qvsdirect.com/Excel-12-W...ainswitch-RCDs-MCBs-Split-5-5-2-pr-23773.html if you must have cheapo Excel stuff.
Was the electrician registered with any of the Part P schemes? Find out and complain very loudly.
You should have had an installation certificate for the change of the consumer unit. Also a Building regulations Completion Certificate.
These will occur because the electrician will have declared that the work he has done complies with BS7671 and Building Regulations Part P. But he hasn't so that is a lie and fraud.
I agree that the appearance isn't conclusive, but the product description in the link provided by the OP is:[Ok, so there's a gap in the mcbs, but that doesnt mean all the circuits aren't rcd protected. Bit odd I admit but not conclusive.
Kind Regards, John.•6 Usable Ways: 3 MCBs on the Mainswitch + 3 MCBs on the RCCD