Hi,
Just wondered if anybody else has had to use these before, and if you would use it?
just asking because, the existing meter cuboard has gas, and electric meter and existing consumer unit.
consumer unit is mounted on the side wall of the cuboard above the gas meter, and at 1 end almost touching the electricity service head... as that is mounted on the back wall... total distance from facing edge of cutout fuse and cuboard door is only 400mm.
width of cuboard is only 500mm.. but 1 corner is completely boxed off because of a soil pipe. So space is very tight and limited... not really my ideal choice for it due to working space but it is where it is.
Presently, it is not 150mm away its more like 50mm..could get round that by insulating the pipes with electrical insulating material but new consumer unit is bigger and just about fits due to it being split load dual rcd, and also splitting some circuits correctly, but even then its doesnt allow for one as big as I would like because there would be no spares.
So can either use 2 smaller consumer units and stack them, or go down the more expensive route of all RCBOs which can use a smaller consumer unit.
Just wondered what other peoples preferences would be.
Just wondered if anybody else has had to use these before, and if you would use it?
just asking because, the existing meter cuboard has gas, and electric meter and existing consumer unit.
consumer unit is mounted on the side wall of the cuboard above the gas meter, and at 1 end almost touching the electricity service head... as that is mounted on the back wall... total distance from facing edge of cutout fuse and cuboard door is only 400mm.
width of cuboard is only 500mm.. but 1 corner is completely boxed off because of a soil pipe. So space is very tight and limited... not really my ideal choice for it due to working space but it is where it is.
BS6891-2005
8.16.2 Separation of installation pipework from other services
Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows:
a) at least 150 mm away from
electricity meters and associated excess current controls, electrical
switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
Presently, it is not 150mm away its more like 50mm..could get round that by insulating the pipes with electrical insulating material but new consumer unit is bigger and just about fits due to it being split load dual rcd, and also splitting some circuits correctly, but even then its doesnt allow for one as big as I would like because there would be no spares.
So can either use 2 smaller consumer units and stack them, or go down the more expensive route of all RCBOs which can use a smaller consumer unit.
Just wondered what other peoples preferences would be.