I have for sometime now been experiencing air problems as per this previous post
I have a Potterton Prima 60F Central Heating system - simple heating system with 16 rads each with TVR so no room stat. Had problems with air in the system for a number of years. Changed the pump approx 6 months ago and since then get a kettling noise above the pump in the feed/expansion area after the system has been running for a couple of hours. I had been advised to check for blockages by placing a magnet on the suspected pipes and the magnet was attracted to the pipe in a number of spots
Added Sentinol X400 and the system ran a lot quieter with minimal air getting into the system. So I thought the X400 had cleared the problem. After flushing the system clean - and it was thoroughly flushed through the system ran well for several hours before the kettling reappeared. The kettling noise reduces when raising the pump speed to 3.
The magnet was still attracted to the same areas of pipe and so I cut out the suspect areas. The 15mm feed pipe was partially blocked in a t piece before the pump. I have replaced this with 22mm pipe thinking that would help after talking to the pump manufacturer - Circulating pumps.
I refilled the system and as normal took me ages to get all the air out of the system. After 48 hours I was pretty sure that all was well as I ran the pump with boiler off and no gurgling noises - the pump ran very quietly with a normal water flow noise in the pipes around the pump.
When I turned the boiler back on the flow noise gradually became noisier when the boiler was firing ie on it's heat cycle. I would not call it kettling more like running water mixed with air. After 4 hours this changed on the heat cycle to more like kettling for 20 seconds then died away as the boiler turned off getting up to heat
One of the suggestions came from gas4you
This test revealed water being sucked up the jar for 1 second and then falling back inot the jar followed by a number of bubbles then the level stayed steady. When I pressed my hand tightly to the bottom of the vent pipe and got my wife to turn the pump on - no noises. Therefore I think my nest step should be to go to combined feed and vent
My system is closely couple as indicated in the following photos
http://i3.photobucket.com/albums/y66/cragga_lfc/dad/CentralHeating004.jpg
This picture is showing left riser from Boiler - top left going to vent - top right cold feed and bottom right into pump ( arrow on the pump pointing down
http://i3.photobucket.com/albums/y66/cragga_lfc/dad/CentralHeating005.jpg
This picture is showing pipes going to the loft where the feed/expansion tank is directly above
On referring to the Potterton Installation & Servicing instructions it suggests an open vented fully pumped system to be fitted with a combined feed & vent.
Could I just remove the vent pipe ie replace left t by dismatling compression fittings above and below and to the right and replace with inverted L ?
I have a Potterton Prima 60F Central Heating system - simple heating system with 16 rads each with TVR so no room stat. Had problems with air in the system for a number of years. Changed the pump approx 6 months ago and since then get a kettling noise above the pump in the feed/expansion area after the system has been running for a couple of hours. I had been advised to check for blockages by placing a magnet on the suspected pipes and the magnet was attracted to the pipe in a number of spots
Added Sentinol X400 and the system ran a lot quieter with minimal air getting into the system. So I thought the X400 had cleared the problem. After flushing the system clean - and it was thoroughly flushed through the system ran well for several hours before the kettling reappeared. The kettling noise reduces when raising the pump speed to 3.
The magnet was still attracted to the same areas of pipe and so I cut out the suspect areas. The 15mm feed pipe was partially blocked in a t piece before the pump. I have replaced this with 22mm pipe thinking that would help after talking to the pump manufacturer - Circulating pumps.
I refilled the system and as normal took me ages to get all the air out of the system. After 48 hours I was pretty sure that all was well as I ran the pump with boiler off and no gurgling noises - the pump ran very quietly with a normal water flow noise in the pipes around the pump.
When I turned the boiler back on the flow noise gradually became noisier when the boiler was firing ie on it's heat cycle. I would not call it kettling more like running water mixed with air. After 4 hours this changed on the heat cycle to more like kettling for 20 seconds then died away as the boiler turned off getting up to heat
One of the suggestions came from gas4you
Perhaps the pipe work vent/feed pipes are incorrectly installed/positioned?
Go into loft and plave a jam jar with water in it over the vent pipe. Get someone to turn on ch and see if water is sucked out of jar into vent?
If so this could be where the air is entering the system.
You could always fit a Myson aerjec where you feed/vent pipes join etc.
__________________
Dave
This test revealed water being sucked up the jar for 1 second and then falling back inot the jar followed by a number of bubbles then the level stayed steady. When I pressed my hand tightly to the bottom of the vent pipe and got my wife to turn the pump on - no noises. Therefore I think my nest step should be to go to combined feed and vent
My system is closely couple as indicated in the following photos
http://i3.photobucket.com/albums/y66/cragga_lfc/dad/CentralHeating004.jpg
This picture is showing left riser from Boiler - top left going to vent - top right cold feed and bottom right into pump ( arrow on the pump pointing down
http://i3.photobucket.com/albums/y66/cragga_lfc/dad/CentralHeating005.jpg
This picture is showing pipes going to the loft where the feed/expansion tank is directly above
On referring to the Potterton Installation & Servicing instructions it suggests an open vented fully pumped system to be fitted with a combined feed & vent.
Could I just remove the vent pipe ie replace left t by dismatling compression fittings above and below and to the right and replace with inverted L ?