You need to improve insulation and draught-proofing as much as is allowed by the building's listed status: consult with any Listed / Conservation Officers as to what's possible to do. That will reduce the heating input needs.
You are currently eating through 45-60MWh per annum in Kerosene? 123-164 kWh/day on average!! Likely to be 3-4x that some days in winter (if not more) and just a few kWh in summer (to top up the HW tank)? That's going to need a bigger than average ashp I suspect and may even require a 3-phase electric supply, ptentially?
NB You ideally don't want (emergency cold backup) immersion heaters in any of the units (nor crankcase 'vampire load' heaters) in the heat pumps - even with stored battery supply. It'll quickly deplete stored energy in colder / darker times when you are using the most energy for heating anyway.
Oil is currently, May 23, under 6p/kWh where I live. Don't forget the true cost of your solar generation should include a capital depreciation (renewal/repairs) and the same for battery storage lifetime. Just like a replacement oil tank at £3k for 10 years life = a £300 pa standing charge: around 3p/kWh for my 1000 litre-ish pa consumption.
CAN you fit air-air or air-water ASHPs to this listed building?? I'd have thought the Planners / Listed Buildings'd not like the look too much?
Mind, if solar panels have been allowed then anything might be OK visually
My a-a pumps will go into defrost mode (but close vents/stop fan on internal units when doing so). They do a defrost when we stop the heating sometimes as you can hear the unit running on after the 'off' is pressed. Minus 12 C: I don't think we've been that cold here so haven't had any problems like you describe so far.
Check out other forums (Moneysaving expert and self build ones where there are threads on ASHPs, designs etc.,.) as well as here.
You are currently eating through 45-60MWh per annum in Kerosene? 123-164 kWh/day on average!! Likely to be 3-4x that some days in winter (if not more) and just a few kWh in summer (to top up the HW tank)? That's going to need a bigger than average ashp I suspect and may even require a 3-phase electric supply, ptentially?
NB You ideally don't want (emergency cold backup) immersion heaters in any of the units (nor crankcase 'vampire load' heaters) in the heat pumps - even with stored battery supply. It'll quickly deplete stored energy in colder / darker times when you are using the most energy for heating anyway.
Oil is currently, May 23, under 6p/kWh where I live. Don't forget the true cost of your solar generation should include a capital depreciation (renewal/repairs) and the same for battery storage lifetime. Just like a replacement oil tank at £3k for 10 years life = a £300 pa standing charge: around 3p/kWh for my 1000 litre-ish pa consumption.
CAN you fit air-air or air-water ASHPs to this listed building?? I'd have thought the Planners / Listed Buildings'd not like the look too much?
Mind, if solar panels have been allowed then anything might be OK visually
My a-a pumps will go into defrost mode (but close vents/stop fan on internal units when doing so). They do a defrost when we stop the heating sometimes as you can hear the unit running on after the 'off' is pressed. Minus 12 C: I don't think we've been that cold here so haven't had any problems like you describe so far.
Check out other forums (Moneysaving expert and self build ones where there are threads on ASHPs, designs etc.,.) as well as here.