Leccy needs to be done before new baby arrives... I can't get an electrician to arrive in time so I've decided to do it myself and get it certificated afters. I'd like to run through what I intend to do and get a 2nd opinion before I start.
I live on the lower ground floor of a divided-up terraced house, i.e. no access to ceiling void. I'm moving my kitchen to a different room. I need a new radial circuit to fit new built-in electric oven (max 2.5kW), new electric hob (max 6.5kW) and microwave (max 1.45kW). TOTAL = 10.45kW
At Consumer Unit, existing cooker control circuit runs off 30A re-wirable fuse. I'd like to...
1) disconnect this, chuck the fuse away and try and label the two ends of the old cable appropriately.
2)replace with 32A MCB, run new 6mm T&E cable to 45A cooker control unit (control switch + [13A]socket). This will be a run of 18.5m via trunking mounted just above the skirting. TOTAL RUN = 20m
3) I'll plug in the microwave at the CCU socket and connect the hob.
4) Run 6mm cable to 13A fused spur, then 2.5mm cable to oven.
5) The CCU will be in prominent position within 2m of the built-in oven & hob.
Will this be certificated as safe or should I be certified insane?
I live on the lower ground floor of a divided-up terraced house, i.e. no access to ceiling void. I'm moving my kitchen to a different room. I need a new radial circuit to fit new built-in electric oven (max 2.5kW), new electric hob (max 6.5kW) and microwave (max 1.45kW). TOTAL = 10.45kW
At Consumer Unit, existing cooker control circuit runs off 30A re-wirable fuse. I'd like to...
1) disconnect this, chuck the fuse away and try and label the two ends of the old cable appropriately.
2)replace with 32A MCB, run new 6mm T&E cable to 45A cooker control unit (control switch + [13A]socket). This will be a run of 18.5m via trunking mounted just above the skirting. TOTAL RUN = 20m
3) I'll plug in the microwave at the CCU socket and connect the hob.
4) Run 6mm cable to 13A fused spur, then 2.5mm cable to oven.
5) The CCU will be in prominent position within 2m of the built-in oven & hob.
Will this be certificated as safe or should I be certified insane?