That, in itself, would not cause the RCD to operate. Immediately the neutral contacts open, no current will flow through either L or N sides of the RCD, even if the L contacts remain closed (hence no imbalance/trip) - unless, as discussed, there is a capacitive path to earth (lower impedance from N than from L).Its probably vaguely possible, opening the neutral first / closing the live first will result in all the wiring of the appliance being at 240v with respect to earth instead of just that on the live side for the short time it takes the other pole to close. Not normally a problem but if there was a high resistance fault on the neutral side to earth then you could get RCD trip if the poles closed in the wrong order.
Kind Regards, John