England was very silly to alter the requirements, especially as doing so all but negated the reason for them in the first place - i.e. controlling DIY and ancillary trades.
Sorry to bring this up again but wanted to check the wiring configuration. I was going to run the 10mm2 cable into one 50A cooker switch then have two seperate cables come out... One to go to a double wall outlet for both single ovens and one to got to a wall outlet for the hob.
However, the hob is 32A and ovens are 13A each so a total of 58A. Do presumably I can't run them both through the one switch?
If I can't, I presume I could have two switches (linked with some 10mm2)...one for ovens and one for hob...?
I was going to run the 10mm2 cable into one 50A cooker switch then have two seperate cables come out... One to go to a double wall outlet for both single ovens and one to got to a wall outlet for the hob.
It doesn't work like that for cooking appliances because they won't all be drawing power at the same time even when/if all are switched on.
"Diversity" is used - 48 x 0.3 + 10 = 24.4A is all you need.
So presumably I can't run them both through the one switch?