Zs on a socket ring circuit (32 A type B MCB TNCS) is 1.5 ohms, which is above the limit in the OSG.
The circuit in question is protected by a 30mA RCD.
I plan to test all the S.O. for loose connections, but does the RCD protection now diminish the importance of the Zs test results.
Any guidance would be appreciated.
Mains voltage fan above shower 220mm from tray, not RCD protected.
If the fan is IPX4 or greater, and was installed on an RCD, would that comply?
The circuit in question is protected by a 30mA RCD.
I plan to test all the S.O. for loose connections, but does the RCD protection now diminish the importance of the Zs test results.
Any guidance would be appreciated.
Mains voltage fan above shower 220mm from tray, not RCD protected.
If the fan is IPX4 or greater, and was installed on an RCD, would that comply?