The point is that you and several others have missed the point of testing entirely.
Continuity tests are done with the system isolated, so whether it's TN-C-S, TN-S or any other system is irrelevant.
Any link between the MET and N will only exist when the system is energised.
There are two correct methods of testing CPC continuity.
One is to attach a long lead to the MET, and confirm continuity between that and earth points at sockets etc. This will detect the fault, as there will be no connection between the MET and the earth of the socket.
The other method involves linking the CPC and line conductor at the consumer unit, then checking at every point for continuity between L&E. This will also detect the fault - as with the previous method, there will be no continuity between L&E at the socket.
Other dubious methods of using a plug with a link inside between L&E at the end of the circuit and then testing at the CU are not suitable, as many faults will go unnoticed.
And yes - it is necessary to check at every single socket, switch, light and other item. Just checking at the end of a circuit proves nothing, it's entirely possible to have CPC continuity from one end of the circuit to the other and yet still have items along that circuit which are not connected. A common example is where a plastic drylining box is used behind a metal accessory, the CPCs are linked in a connector, but there is no connection from that to the accessory. Usually occurs when a plastic switch is changed to a metal one. The same can happen when ceiling roses are changed to fancy lights which require separate connections in the ceiling.
If some buffoon decided to just 'test' an installation by ignoring most of the tests and just checking for Zs at the socket, this type of fault would not be found. However neither would most other faults, making the whole procedure totally irrelevant.
If any test was to be ignored, then it should be Zs - if other tests have been done correctly, Zs is only confirmation of an already known fact.
Manufacturers of test equipment do not agree - hence the proliferation of 'no trip' loop testing using only a few mA, and those
overpriced adaptor pieces for the inexplicable situation where a 3 wire Zs test is needed at a ceiling rose.