cross bonding confusion

Joined
15 Apr 2005
Messages
16
Reaction score
0
Country
United Kingdom
if my property has a 4mm continous earth cross bonding my water pipes to the boiler and water stop cock, do i need to return the earth back to the consumer unit(like a ring main)? :confused:
 
Sponsored Links
diydamian said:
if my property has a 4mm continous earth cross bonding my water pipes to the boiler and water stop cock, do i need to return the earth back to the consumer unit(like a ring main)? :confused:

no. its just accross the pipes. the main gas and water should also be earthed with 10mm min (6 for TT). this is taken back to the MET
 
so separate 10mm earths to the water and gas mains would be suffecient?
 
diydamian said:
so separate 10mm earths to the water and gas mains would be suffecient?
you need to bond gas and water (and oil /structural steel if used). you should also cross bond pipes at boilers
 
Sponsored Links
diydamian said:
so separate 10mm earths to the water and gas mains would be suffecient?
Ask your electricity supplier as they may require you to put 16mm² main equipotential bonding in.
 
Yeah, I get confused. Do I wear the basque or fish-nets?

Oh *it!! You said cross bonding, I thought you said cross-dressing..... :oops:
 