Is that an apology then, as I find the "C" word to be very insulting !
No - it's me explaining that I was saying
IF you spuriously said to a customer "it's the regs - they've changed, it's going to cost you more" then you would be a c*****.
Whether its a 3 part or one part, the fact remains that other than only for a PIR where LIM or X can be entered, you must enter a tick to say the result is satisfactory.
You need to look more closely at the bottom of the Schedule Of Inspections....
Your argument therefore would mean that all inspections and tests relate, in this instance of a CU change, only to the actual consumer unit installation, and not the final circuits, which I think is unacceptable.
Explain how most of the inspections relate to the actual job of a CU change. I'm not saying don't do them, but whatever you find when you do them is not a finding that results from what
you are doing.
You are replacing the CU, so it is that job where you have to ensure that what you do complies with BS7671, and when you are testing and inspecting the existing wiring, you have to ensure that the testing and inspecting complies with BS7671, but you have no control over, and no responsibility for, what you find.
Forget the 17th and RCDs for a minute - if you're replacing a CU, and you find that a cable is incorrectly routed, then what can you possibly put on the EIC except an X in Box (a) under Cables and conductors?
Your sense of professionalism and ethics will determine what you actually do about it, but the regulations do not require you to remove and re-route the cable, or to refuse to connect that one to the CU, or to refuse to do the job at all.
Back to the original question, when changing a CU post July 2008, do all circuits with concealed cables < 50mm require RCD protection ?
I think the answer to that comes naturally when you consider these scenarios pre-17th:
When changing a CU, and you find a 2.5mm² radial on a B32, do you put it back on a B32, or change to a B20/B16?
When changing a CU, and you find that sockets reasonably expected to supply portable equipment outdoors are not RCD protected, do you leave them like that, or put them on an RCD?
When changing a CU, and you find that its a TT installation with no RCD incomer, do you leave it like that or put one in?
You are responsible for installing a CU which provides protection in accordance with the regulations.
I will try the NICEIC for their stance.
OK, but remember they like to think, erroneously, that they write the regs....