I apologize, it was meant to be 6mm not 16mm
Many other sizes of cable are available.
As for the size and type required:
- what is the total load for this new consumer unit
- how long is the cable from the supply to the consumer unit
- how / where will the cable be installed
- what type of earthing is provided at the supply
- what will the cable be connected to at the supply end
- are there any extraneous conductive parts at the office/garage?
When you did that did you have good cause to believe that the fault loop impedance would be OK? "what's already there has been there for X number of years and inspected and passed testing annually" is irrelevant - you were responsible for the new stuff.I've installed a ring to the garage with a few more sockets and a new ring in the office with more sockets to eliminate the need of four ways connects to four ways.
Not an answer to the question you've been asked. You still have no idea what it meant, you still have no idea why it matters. You still do not understand the problem of unknown unknowns.The supply from the house is earth via the earth bar at the top of the cu and that follow through to the first socket in the garage.
My understanding is clearly wrong in terms of conductive parts, I assumed it was something that could become live if a fault is present hence why I said, cables are covered with conduit, metal cu will be earthed.
You've already shown that you have some dodgy misconceptions - what if you get something wrong because you have no idea your knowledge is wrong? What if you miss something because you simply have no idea it even exists, and just don't realise you don't know it?
Have him instruct and supervise you as he sees fit - it will be his name on the paperwork.I do understand that an electrician is required, and one will be here next week, but I would rather do as much as I can myself to lower costs.
I get your point,
?? According to who?In case you think this is a technicality, think on- you could be charged with causing criminal damage (which is a proper crime rather than a civil offence), you could be evicted for breaching the terms of your tenancy AND find yourself ineligible for assistance from your local council (due to intentionally making yourself homeless by breaching the terms of your lease)
I won't be testing it, I will be getting a electrician in to inspect and test but obviously want to save as much as possible
Installing the consumer unit was easy, installing the ring circuit and sockets was easy, I'm simply asking a question as to which is best practice, 10mm or 16mm armoured.
The 32amp in the house which currently feeds everything but o my if I plug in the circlular saw at 2600w and a 1200w Hoover, but I think it's because the socket they are plugged into runs of a plug plugged into another socket .
The trip isn't the issue tho once I've connected the new board up as I don't think it's caused by the 6mm cable