Hi I am a retired degree qualified electrical and electronics engineer. I help out at my daughters exotic animal rescue/sanctuary.
Apologies for long post .
Unfortunately most of the animal enclosures require heating and at the moment use (expensive) electrical heating. We have been looking at power use with a clamp on ac ammeter ( and I’m looking at a better data logging option so we can evaluate solar etc.
Site is large (think farm size) and rural but has single phase supply and TN-C-S / pme with satisfactory fixed wiring report. Quite a few long SWA runs to out buildings each using TT with rods.
While looking at currents on main incoming tails and clamping line ,neutral and main earth there is a net current of the order of 17 amps with something like 55 amps line current. This seems odd to me and I even did the same check on my home installation where reading was zero ( 20A range ) as I’d expect.
It’s quite tricky to monitor readings due to number of loads switching on thermostats but I do intend to check line - neutral and neutral - earth voltages next time I’m there.
any comments.
Apologies for long post .
Unfortunately most of the animal enclosures require heating and at the moment use (expensive) electrical heating. We have been looking at power use with a clamp on ac ammeter ( and I’m looking at a better data logging option so we can evaluate solar etc.
Site is large (think farm size) and rural but has single phase supply and TN-C-S / pme with satisfactory fixed wiring report. Quite a few long SWA runs to out buildings each using TT with rods.
While looking at currents on main incoming tails and clamping line ,neutral and main earth there is a net current of the order of 17 amps with something like 55 amps line current. This seems odd to me and I even did the same check on my home installation where reading was zero ( 20A range ) as I’d expect.
It’s quite tricky to monitor readings due to number of loads switching on thermostats but I do intend to check line - neutral and neutral - earth voltages next time I’m there.
any comments.