Hi, in the coming months there will be a job which involves installation of a Server Rack. So i was just wondering what kind of requirements are required, and the regulations.
I understand the rack needs to be properly earth bonded, and that it would need its own separate electrical ring circuit, probably at least around 40Amp 6mm cable, along with a 50amp MCB, and RCD setup.. if incorrect please correct me. With probably an industrial 3pin 63Amp plug and socket and a 3 pole isolator, 63Amp because 1 down from that is only 32amp
Cable probably ideally should be 40Amp 6mm cable with a 50 amp mcb and dedicated earth for the Rack.
as at maximum load, the 3 severs which have the 10amp warning sticker alone would add up to 30Amp.
If thats under-rated or over rated any recomendations?
although not at present, the final setup will be anything up to,
2 Swiches, Modem, VPN Firewall
3 or 4 Servers 2/3 of which according to the power supply sticker, at full load use 10 amp each. Because there is a warning sticker on it saying
(It is dangerous if the wall socket is not specified for 250vac/10amp)
and a UPS
and that should allow for sufficient expansion?
I understand the rack needs to be properly earth bonded, and that it would need its own separate electrical ring circuit, probably at least around 40Amp 6mm cable, along with a 50amp MCB, and RCD setup.. if incorrect please correct me. With probably an industrial 3pin 63Amp plug and socket and a 3 pole isolator, 63Amp because 1 down from that is only 32amp
Cable probably ideally should be 40Amp 6mm cable with a 50 amp mcb and dedicated earth for the Rack.
as at maximum load, the 3 severs which have the 10amp warning sticker alone would add up to 30Amp.
If thats under-rated or over rated any recomendations?
although not at present, the final setup will be anything up to,
2 Swiches, Modem, VPN Firewall
3 or 4 Servers 2/3 of which according to the power supply sticker, at full load use 10 amp each. Because there is a warning sticker on it saying
(It is dangerous if the wall socket is not specified for 250vac/10amp)
and a UPS
and that should allow for sufficient expansion?