When I use Alphatek, the RCD trip times can be very different with stuff plugged in.
End to end yea, similar technique to the OSG. No clips = holding cable with thumb against probe tip. Instructor at college is not a fan of croc clips so taught us this way.
I'm not getting how something 'plugged in' is causing a rise in the resistance reading on a R1 + R2 test.
Anyone care to explain??
By the way you are not spliting the ring final circuit into two 20Amp radials for testing you are just splitting the ring final circuit..
Surely this would give me one socket as higher than the others / unless they're all faulty. I suspect the outside socket needs replacing.It is always possible that the socket itself is the problem.
The thought had crossed my mind, but this is the only test it's having problems with, All the other rings went fine. And have gone back to one and it's still fine.or you have a faulty tester.
Possibly user error yesterday. I was much more thorough today than yesterday, and double / triple checked some results.I don't have an answer, but -
Why has the r1+rn gone up from spot on 0.26 yesterday to 0.32-0.39 (excl. spur)?
I'm a bit suspicious that the r1+r2 results are (exactly) one hundred times higher than they should be.
Does that help ???
Out of interest, have you taken a r1+r2 reading at the in/out-coming legs points at the CU, also have you taken any test with socket fronts off, testing across terminal points?
I mean't, where you have cross connected the two legs of r1 and r2.Not sure what the first part of that means, but yes I have confirmed across terminal points.
Is there a design reason to do this because unless you or your electrician resolve the problem - the problem will still remain.I mean with my new consumer unit, split this ring into 2 x 20a radials. For functional use not for testing. Obviously I will try the splitting into two radials for testing purposes too.By the way you are not spliting the ring final circuit into two 20Amp radials for testing you are just splitting the ring final circuit..
You will only gain experience by following the correct testing procedure in the correct order - rather than trying to guess what the problem might be.[0.53x1.67=0.89 ohms. Meaning the cpc is only 0.05 away from calculated for end to end, which is within tolerance. Just can't get my head around the massive difference & don't understand how it can happen. It's all about experience I guess
I mean't, where you have cross connected the two legs of r1 and r2.
Have taken a reading at that point, across the two legs at the CU, as if it where a socket outlet?
Is there a design reason to do this because unless you or your electrician resolve the problem - the problem will still remain.
You will only gain experience by following the correct testing procedure in the correct order - rather than trying to guess what the problem might be.