I'm not sure what you mean by a 'dedicated appliance', but if you're talking about an appliance protected by a 13A fuse (in a plug or fused connection unit), then you need at least 1.25mm² flex, usually 1.5mm². Whether or not it needs to be heat-resistant flex depends upon exactly what the appliance is, and where the flex will be sited.What flex should be put on a 13amp dedicated appliance?
What's a dedicated appliance?
You may be right, but it's also possible that Granny left first!Bet it left in the end, though.
The size and type of cable stated by the manufacturer.
At a 13amp load, 1.5mm² may be OK if the cable length is relatively short. Longer lengths of cable run, or cables in warm environments may mean a larger csa is needed.
Would that be marked CE ?0r a 0.25 mm² flex on China Export?
Fair enough but can you be certain?Now come on lads the BS7671:2008 is the one which refers to dedicated supply and saying appliance instead of supply is clearly just a slip up.
It could be protected by a BS3036 and require derating.Table 4F3A states 1.25 mm² for 13A single phase a.c. for flexible cord.
I know you find lead sets with 10A IEC sockets and 13A Plugs with 0.75mm² cable but that does not mean it's allowed. Even 10A requires 1 mm² cable and I think the moulded plug and socket leads with 0.75 mm² cable are designed as computer supplies and not kettle supply. I know the notch is normally found with the kettle (C15 - C16) which will take the higher temperature but the (C13 - C4) IEC lead is still rated 10A as is the (C15 - C16) non of them are rated at 13A so should only be used up to 2.3kW however since a kettle boils in just a few minutes there is not really a problem with such a short time of overload.The size and type of cable stated by the manufacturer.
At a 13amp load, 1.5mm² may be OK if the cable length is relatively short. Longer lengths of cable run, or cables in warm environments may mean a larger csa is needed.
Or a 0.75mm^2 cable not exceeding 2m in length fitted with a moulded plug?
Or a 0.75mm^2 cable not exceeding 2m in length fitted with a moulded plug?
That sounds very reasonable.Towards the end of my career, I saw many (often brand new) appliances with 0.75 flex and moulded plugs, fitted with 13A fuses and, rightly or wrongly, I failed them when PAT testing or called them into question when coming across them on other jobs, simply because 0.75 did not equal 13A according to 7671.
I'm struggling a bit Does anyone have access to "Table 2 of BS1363-1" (and associated text)? [and is an "18W fridge-freezer" a bit optimistic?? - I'm not sure that would cover the lights in mine!]This from an IEE thread:
.... So, 18W fridge freezer, 0.75 sq mm flex, 13A fuse, is quite safe and acceptable provided the flex length is below the limit in Table 2 of BS1363-1.