Thanks. Does the associated text help to make any sense of it?Invoking the fair quotation law:...
I'm struggling a bit
Indeed- as I indicated at a start, that's what BS7671 says.So, 1.25mm² minimum for a 13amp load.
As we've often discussed, even if the (normal) load is less than 13A, BS7671 would, I think, still require 1.25mm² minimum unless (a) it could be successfully argued that the nature of the load was such that it could not create an overload and (b) (probably usually satisfied) there was adequate fault protection for the cable. Of course, some will even debate whether appliances flexes come within the scope of BS7671 - but that seems a bit silly to me, particularly in the case of a hard-wired appliance.That's assuming the load really is 13amp.
Given that it's only about 24 hours, there are probably plenty of other possible explanations - not everyone spends their entire life in front of a computer I would personally be inclined to wait a bit longer before getting too critical!... But as the OP has contributed ZERO since his original post, I conclude that he is no longer interested, or his house has burnt down
Does the associated text help to make any sense of it?
Don't worry, I don't shoot messengers (not the least because I am often 'the messenger' myself, and hence hope that others will follow my non-shooting example ). In any event, we now seem to have established that BS1363-1 does, indeed, say these things in its Table 2 - but, as I've said, I think we now need to discover whether the associated text helps to make any sense of it!Don't shoot the messenger!!I'm struggling a bit
Thanks again. However, I'm not sure that qualifies as 'helping to make any sense of it" - if anything, it raises even more questions!Along the lines of: "If a plug wired on to the end of a cable is not supplied for a specific use then the free end shall be marked with the maximum current that the equipment it is wired to is allowed to take, according to table 2.Does the associated text help to make any sense of it?
Is that a UK law, or a US one?Invoking the fair quotation law
UK - usually known as 'Fair Dealing'. Yes I didn't mention the source, but that was obvious in context.Is that a UK law, or a US one?Invoking the fair quotation law
If by 'IET rules' you are referring to the guidance in ('informative') Appendix 15 of BS7671 about measures which are advised for avoiding overloading of a ring final circuit, all it suggests is that cooking appliances >2kW should not be supplied by a ring final - but, instead, should have dedicated circuits. It says nothing about not using plugs/sockets.... it states IEE rules must be followed yet it says it can be plugged in like a kettle and since over 2kW that would not be in-keeping with today's IET rules.