Vaillant 428 - Min flow required approx 20 litres/min (0.33 litres/sec or 1200kg/h)
Pump Grundfoss Selectric 15/50 (set at III) - Pump curve here: http://www.plumbnation.co.uk/site/g...ump/Grundfos UPS Selectric Pumps Brochure.pdf
ABV Honeywell DU144 - Curve here: http://products.ecc.emea.honeywell.com/europe/pdf/du144-pd-en0h2706ge25r1208.pdf
If I've got the theory right, the min pump flow puts the head/pressure at around 3.3m, approx 32kpa (or 320mbar) on the Grundfoss chart.
32mbar head and 1200kg/h flow on the Honeywell chart would look to me to be about 0.08.
So from that, theoretically this setup above the ABV should be set wound pretty much all the way out (scale of 0.1 - 0.6).
Have I got that right?
Pump Grundfoss Selectric 15/50 (set at III) - Pump curve here: http://www.plumbnation.co.uk/site/g...ump/Grundfos UPS Selectric Pumps Brochure.pdf
ABV Honeywell DU144 - Curve here: http://products.ecc.emea.honeywell.com/europe/pdf/du144-pd-en0h2706ge25r1208.pdf
If I've got the theory right, the min pump flow puts the head/pressure at around 3.3m, approx 32kpa (or 320mbar) on the Grundfoss chart.
32mbar head and 1200kg/h flow on the Honeywell chart would look to me to be about 0.08.
So from that, theoretically this setup above the ABV should be set wound pretty much all the way out (scale of 0.1 - 0.6).
Have I got that right?