Dimmable CFL and buzzing from MCB
18 Mar 2008
Sussex
Hi
I have installed 7 Dimmable low energy lights (Megaman GU10 Dimmable 11 watt each), with a 1Kw Varilight Dimmer
I have checked the minimum and maximum lamps and I am ok on this front. However when I switch the lamps on there is a distinct buzz coming from the MCB.
The CU is brand new and I had it checked out by the elctrician who installed it and he says all is fine.
Is it the same as this post: //www.diynot.com/forums/viewtopic.php?t=127376 ???
and if so is there anything I can do about it?
Regards
Ron
Hi.......just wondering why with only 7 'low energy' lamps you require such a huge dimmer??...........you may have an underloading problem.
No, the rating for dimmers are not straightforward, minimum load is for the lamps should not fall below 1/6 of the min load (in this case 200/6 = 33, with 7 lamps we have 77W so this is ok)
Max wattage is similar but not to exceed 1/5, i.e. 1000 * 1/5 = 200 (so 77W is ok for this too.
Regards
R
