Hi,
I have a new-build with (just about) attached garage which has one double socket and one light socket installed.
The double socket is connected via a spur from the ring main for the downstairs sockets using a single 2.5mm T&E cable through the wall to the main house. Downstairs sockets are on 32A breaker in CU.
Likewise the light socket is connected via a spur from the downstairs lighting circuit, through the wall on a single 1mm T&E cable. Downstairs lights are on 6A breaker in CU.
It's challenging to get any more cable from the main house into the garage.
I am adding a bunch of extra sockets (using more 2.5mm cable) and lights (using more 1mm cable) in the garage. HOWEVER I am adding the sockets for convenience and I won't be using more than 13A (or maybe 16A) in total at any one time in the garage.
So I have bought a small garage Consumer Unit with 16A and 6A MCBs (also an RCD which I won't be using, there are two RCDs in the main house CU already). My plan is to add this little CU where the two sets of T&A cable come into the garage. Then, I believe I can safely add as many sockets and lights as I like despite them connecting via spurs.
I'm pretty happy this is safe. What I don't know is whether it meets regs.
My understanding regarding the regs is that if I were adding a 13A fuse where the spur comes into the garage, my setup would comply (conceptually all the sockets are then like a fused 13A extension lead).
Firstly, am I right about that?
Secondly, can I use the CU I've bought with its 16A MCB instead of the 13A fuse? If not, would a 13A MCB do the job, or would it have to be a fuse for some reason?
Thirdly, same question for the lights and the 6A MCB. Valid/too high/needs to be a fuse?
I really appreciate any guidance.
Oh and when I say "comply" I mean "comply after a qualified electrician has signed off on it", but I'd like to get the installation right myself first.
Thanks in advance
I have a new-build with (just about) attached garage which has one double socket and one light socket installed.
The double socket is connected via a spur from the ring main for the downstairs sockets using a single 2.5mm T&E cable through the wall to the main house. Downstairs sockets are on 32A breaker in CU.
Likewise the light socket is connected via a spur from the downstairs lighting circuit, through the wall on a single 1mm T&E cable. Downstairs lights are on 6A breaker in CU.
It's challenging to get any more cable from the main house into the garage.
I am adding a bunch of extra sockets (using more 2.5mm cable) and lights (using more 1mm cable) in the garage. HOWEVER I am adding the sockets for convenience and I won't be using more than 13A (or maybe 16A) in total at any one time in the garage.
So I have bought a small garage Consumer Unit with 16A and 6A MCBs (also an RCD which I won't be using, there are two RCDs in the main house CU already). My plan is to add this little CU where the two sets of T&A cable come into the garage. Then, I believe I can safely add as many sockets and lights as I like despite them connecting via spurs.
I'm pretty happy this is safe. What I don't know is whether it meets regs.
My understanding regarding the regs is that if I were adding a 13A fuse where the spur comes into the garage, my setup would comply (conceptually all the sockets are then like a fused 13A extension lead).
Firstly, am I right about that?
Secondly, can I use the CU I've bought with its 16A MCB instead of the 13A fuse? If not, would a 13A MCB do the job, or would it have to be a fuse for some reason?
Thirdly, same question for the lights and the 6A MCB. Valid/too high/needs to be a fuse?
I really appreciate any guidance.
Oh and when I say "comply" I mean "comply after a qualified electrician has signed off on it", but I'd like to get the installation right myself first.