I live in Croatia but own a small cottage in Scotland that I rent out. My Landlord Registration is due for renewal soon and I have to provide various documents including an electrical safety report. I got an electrician to inspect the property but he has found various defects. His estimate for rectifying these is £1650 including VAT. A big chunk of that is for renewing 3 consumer units. There is one for the main house, one in the garage and one in an attached outbuilding which houses the gas boiler. The one in the garage is a purpose made Screwfix garage CU with RCD and MCBs for lights and sockets. He says that should have a metal enclosure and the RCD and MCBs should be the same make (one MCB is Volex, I think the rest is Protek). The other 2 are older and I think are still fuseboxes, with no RCD. He says RCD protection is required because of regulation 522.6.202/203. This regulation concerns cables behind plaster, panelling or whatever. Has this regulation been applied retrospectively, to old installations? If so, it implies that every home with no RCD protection is deemed unsatisfactory.
 
If your renting out, it is probably very wise to have an RCD and a new main CU.

I think its a bit silly having new CUs in the out buildings however. Dends on cost&labour I guess
 
The fact that there is three consumer units that tells me your original CU is ancient and can't be altered. So either you or someone else decided to save money and cause problems in future.

The one in the garage is a purpose made Screwfix garage CU with RCD and MCBs for lights and sockets. He says that should have a metal enclosure
Debatable.
and the RCD and MCBs should be the same make (one MCB is Volex, I think the rest is Protek).
True. However a new consumer unit won't be needed, just a replacement of the MCB will be fine.
The other 2 are older and I think are still fuseboxes, with no RCD. He says RCD protection is required
What code does the EICR say about this? Send a picture.
 
In 2008 the rules on bonding in a bathroom changed, what is required depends on if RCD protected or not, and it is getting harder and harder to ensure bonding complies with pre-2008 rules. So the only safe way is all circuits to be RCD protected.

If an RCD trips, that can cost you in call out fees, so in real terms you want a system in which the RCD is less likely to trip, and if it should trip, less likely to result in a call-out. So it is likely prudent to go down the all RCBO route, even if one can technically get out of it, not worth the hassle a twin RCD system can cause in the future.

As to surge protection devices, (SPD) we are support to explain the advantage of having them fitted, but the owner can refuse them. The problem with that, is as a retired electrician I am not convinced we need them, so how can I persuade someone else? It seems likely they can reduce LED lights failing etc, but not seen anything which proves that.

As to if you must fit RCD protection, I would say, would I want to stand in court and try to argue they were not required, if something goes wrong, and the answer is no, I would prefer to say I did all I could to make the home safe. The phrase is "potential danger" can we ever say 230 volt supply is without some potential danger? Of course there is danger, people will do silly things,
IMGP8427.jpg
why would anyone put a plug in a socket like that to open the shutters, would I ban all socket extensions of that design, no I would not, but I have seen where people have got very worried about unshuttered sockets. Some common sense is required, and the risk assessed.
 
An update on this. I submitted the inspection report as it was, together with various other documents to support my application for landlord registration renewal. Today I had an email saying the registration is approved. I don't know whether that means I will hear no more for another 3 years or will they still come back and demand the (alleged) electrical defects be put right?
 
An EICR is a snapshot of the installation on a particular date. If you EICR today says "Satisfactory" then that is it, for now.

HOWEVER (there's always at least one)

The Electrical Safety Standards in the Private Rented Sector Regulations 2020 require that an EICR is carried out at an interval of at least every 5 years. It is recommended also that an EICR is done at change of tenancy.

 
The Electrical Safety Standards in the Private Rented Sector Regulations 2020
Applies to England.
own a small cottage in Scotland that I rent out
I have the same problem here in Wales, our rules and regulations are similar to England, but not the same.

If I do a google here for if repeater signs are needed to 20 MPH speed limits, I get
No, 20 mph speed limits do not need repeater signs because 20 mph is the default speed limit in built-up areas with streetlights.

Has it detected I live in Wales?

But continue reading, and it says
20 mph zones also require repeater signs or roundel road markings at regular intervals.
so I am non the wiser!
 
Why have we gone from EICRs in Scotland to speed sign rules in Wales?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top