CE is not a certification. It is a maker's claim. Sometimes it is untrue.
 
Sponsored Links
So I said to you what you said to Eric, but as you hadn't bought any that makes me a pedant who should sling his hook.

Eric hasn't bought any either, so what does that make you?

Feel free to be rational and consistent when replying.
 
I don't need to justify anything to you, but just you keen posting your pedantic nitpicking drivel
 
I hope you are very grateful that you don't need to justify anything, given that you are totally unable to.
 
I found this online and they are saying suitable for 48v DC
would using 12v cause any problems
I did a quick test on a 6amp breaker today using 12v DC it tripped out at around 8 amps ?
image.png
 
I found this online and they are saying suitable for 48v DC
would using 12v cause any problems
No. 48 will be a maximum.

I did a quick test on a 6amp breaker today using 12v DC it tripped out at around 8 amps ?
They work by heat - imagine a fuse.
Not possible to be able to carry 6A with no damage and then trip on 6.1A.

MCBs should not trip at up to 1.13 times their rating and
in 60 minutes at 1.45 times their rating.
Above that progressively quicker until
for B type - in 0.1 seconds at 5 times their rating.
 