You are seemingly a 'man of faith'.... Also, all the houses I've lived in have been new builds, so haven't had botched wiring
Kind Regards, John
You are seemingly a 'man of faith'.... Also, all the houses I've lived in have been new builds, so haven't had botched wiring
You now know better.Thanks, I understand what you are saying about Fused Spurs and spurs. It has always seemed a little strange calling an FCU a fused spur, but as you say this tends to be what the laymen knows them as (including myself).
Ok, but how else could you have a fused spur (the cable)?Regarding a spur that is fused (connected to an FCU), this is the first time I have come across this, but that's probably because I don't really do much with electrics.
I don't think so.Out of interest, is there a "better" way (I guess that would mean safer way) to wire up these sockets?
At counter level there are three sockets next to each other:
Fused Spur Switch 1 | Fused Spur Switch 2 | Double Socket
Ok, but how else could you have a fused spur (the cable)?
It depends what you are meaning by 'sockets'.
Even the sellers do not call FCUs sockets.
That is true, provided that there is only one socket (an 'unfused spur'). If more than one socket (or a socket plus 'other things') is supplied by a spur cable from a ring (and 2.5mm² cable is being used for the spur), then there has to be an FCU to 'limit' the total current draw of all the spurred sockets etc. to 13A.I meant I hadn't ever considered that a spur socket would need to be fused i.e. connected to a FCU. I assumed that a single cable would be run from another socket to the new spur or a terminal block would be used to connect the new spur upto the ring circuit. In either case there is no FCU.
That is true, provided that there is only one socket (an 'unfused spur'). If more than one socket (or a socket plus 'other things') is supplied by a spur cable from a ring (and 2.5mm² cable is being used for the spur), then there has to be an FCU to 'limit' the total current draw of all the spurred sockets etc. to 13A.
Kind Regards, John
Quite so - as I wrote ...Unless, of course, you use a cable suitable for the 32A - 4mm².
If more than one socket (or a socket plus 'other things') is supplied by a spur cable from a ring (and 2.5mm² cable is being used for the spur), then there has to be an FCU ...
Not really; the cable can take 27A. That's why a double socket is allowed.I suppose a spur with a 2.5mm cable going to a double socket could potentially overload the cable if a 3kw heater was plugged into both of the sockets.....
4mm² can take 37A, but it is more than the 32A of the MCB, so more than one double socket would be compliant.Whereas as EFLI says if it was connected by a 4mm cable then that cable would have a limit of 32A and the MCB at the CU then protects the cable from overload.
Unless, of course, you use a cable suitable for the 32A - 4mm².
3kW is about 13A. 2 x 13A = 26A. The current carrying capacity of 2.5mm² cable (installed 'Method C, as most commonly) is 27A, hence, since 27 is more than 26, no problemI suppose a spur with a 2.5mm cable going to a double socket could potentially overload the cable if a 3kw heater was plugged into both of the sockets.....
Indeed - if one uses 4mm² cable for the spur (again, Method C), then, as far as the spur cable is concerned, the spur can supply as many sockets as one wants (with a 32A MCB). However, very few people, including many electricians, really think of that possibility - they have merely learned that "an unfused spur must not supply more than one socket", without having given any thought to the matter of cable size.Whereas as EFLI says if it was connected by a 4mm cable then that cable would have a limit of 32A and the MCB at the CU then protects the cable from overload.
Do you mean a 4mm cable from the consumer unit i.e. for the ring circuit, not just 4mm cable for the spur part?
Sort of. It won't be on the limit of the 4mm² (37A) but the limit of the MCB (32A).So the 2.5mm ring cable isn't likely to be affected if the load on the spur(s) is at the limit of the 4mm spur cable?
Both. With the proviso, as John said, that the full load should not be near either end of the ring.Is this because the 2.5mm cable is on a ring i.e. both ends of the cable are connected to the consumer unit? Or is this because the MCB would trip and protect the 2.5mm ring cable?