That seems fine to me.
Are you thinking about the possibility of exposed/accessible live parts? If there aren't any of those, then my understanding was that any device could/would be Class I if any/all exposed-conductive-parts were earthed. Is that not correct?By using these devices with 230V you are removing the SELV safety barrier and are converting them to an environment that they are not designed for. ... If you earth the case then you are assuming they can be a Class I device, they may not be.
Again are you perhaps talking about the possible presence of exposed/accessible live parts? If not, what tests (and what results of those tests) would indicate to you that the exposed metal parts of this fitting (which, as you've said, is clearly not Class II) should not be earthed? Since it is clearly not Class II, one thing which is surely clear is that the OP's fitting could not be used at 230V without the exposed metal parts being earthed.Without stringent testing, it is impossible to state if the case should be earthed, or not.
Same question, again, I suppose - are you just thinking of the possibility of exposed/accessible live parts? In the absence of that, my understanding was that Class III merely meant that, because of the SELV supply, a Class III device is not required to have the protective measures necessary for it to be either a Class II device (i.e. double insulation or equivalent) or a Class I device (i.e. earthing of all exposed-conductive-parts). Hence, my understanding was that, in the absence of exposed/accessible live parts, if one earths the exposed-c-ps of a Class III device, it becomes a Class I device. Is that wrong?The link that you supplied for these Aurora fittings says that they are CLASS III devices.
Have you got all that the right way round?Are you thinking about the possibility of exposed/accessible live parts? If there aren't any of those, then my understanding was that any device could/would be Class I if any/all exposed-conductive-parts were earthed. Is that not correct?By using these devices with 230V you are removing the SELV safety barrier and are converting them to an environment that they are not designed for. ... If you earth the case then you are assuming they can be a Class I device, they may not be.
Agreed.Again are you perhaps talking about the possible presence of exposed/accessible live parts? If not, what tests (and what results of those tests) would indicate to you that the exposed metal parts of this fitting (which, as you've said, is clearly not Class II) should not be earthed? Since it is clearly not Class II, one thing which is surely clear is that the OP's fitting could not be used at 230V without the exposed metal parts being earthed.Without stringent testing, it is impossible to state if the case should be earthed, or not.
I don't think you have explained/asked very well.Same question, again, I suppose - are you just thinking of the possibility of exposed/accessible live parts? In the absence of that, my understanding was that Class III merely meant that, because of the SELV supply, a Class III device is not required to have the protective measures necessary for it to be either a Class II device (i.e. double insulation or equivalent) or a Class I device (i.e. earthing of all exposed-conductive-parts). Hence, my understanding was that, in the absence of exposed/accessible live parts, if one earths the exposed-c-ps of a Class III device, it becomes a Class I device. Is that wrong?The link that you supplied for these Aurora fittings says that they are CLASS III devices.
I think I have got it the right way around in my mind, but maybe that's not clear from what I wrote! What I mean is that IF a device has exposed-c-ps and IF it is not Class II or III then it is Class I IF those exposed-c-ps are (as required) earthed. My understanding is that there is not necessarily any difference (of design/construction) between a Class 0 and Class I device, the distinction really depending upon whether or not the exposed-c-ps are earthed. In other words, if one took a (probably 'not permitted') "Class 0" appliance and earthed it's exposed-c-ps, would it not become Class I (and 'permitted')?Have you got all that the right way round?Are you thinking about the possibility of exposed/accessible live parts? If there aren't any of those, then my understanding was that any device could/would be Class I if any/all exposed-conductive-parts were earthed. Is that not correct?
Again, I probably expressed myself badly (it was late at night ) ....Surely the classifications are determined the other way round? ....
Indeed - although, as above, it would seem that an identical appliance could satisfy the definition of Class 0 (and thereby almost certainly not be permitted) if it were not earthed.That is, an appliance is Class I because it requires earthing - not because it is earthed.
It's obviously true that a Class II appliance is Class II because of the double insulation (or equivalent). I'm not so sure about "should not be earthed". If there are extraneous-c-ps ('outside' of the double insulation), I don't think there is any prohibition from earthing them (not that there would be any point), is there?Similarly, a Class II appliance is so because it is double insulated and should not be earthed - not because it is not earthed.
Again, yes, that's obviously why it's Class III, but my comment/question about "should not be earthed" again apply. Are you suggesting that if, whilst it was still SELV, some regulations would have been violated had the exposed-c-ps been earthed?Also, a Class III appliance is so because it is SELV and should not be earthed - not because it is not earthed.
I agree.I can see nothing wrong with what the OP has done (G/Y sleeving apart). ... The parts are clearly the same.
Quite - at least, in order to be permitted. As above, if one changed from SELV to 230V without adding the earthing, would effectively have a (non-permitted) Class 0 device.The parts are clearly the same. Changing the item form SELV to 240V with a single insulated connector would mean it is now Class I and must be earthed.
Fair enough. Within a few months, you will hopefully be able to exercise more discretion in relation to MIs and still be compliant with BS7671.I agree. My purpose for being pedantic is that we usually hold up the MI's as THE instruction for the product. Indeed, BS7671 requires this. This product is a Class III product.
True, but there is a very limited number of classes to choose from. If this fitting were not used at SELV, it could not be Class III, and clearly is not Class II, and to say that it did not require an earth (Class 0) would not be permitted - so, unless you are suggesting that there are some devices/appliances/fittings which are 'classless', I can't see what it could be, when used at 230V, other than Class I (requiring exposed-c-ps to be earthed).There is always a risk when providing 230v devices inside a metal container. That is why manufacturers determine which class the product is, and provide connections instructions that are appropriate.
I would say that it's much stronger than just your personal view. By effectively converting the fitting into a Class I one, the OP will have surely made it (in anyone's eyes) essential that the exposed-c-ps be earthed, won't he?Personally, I would want to see the metal case earthed in this modified product. At least the fault path will be to earth, should a supply connection chafe and make contact with the downlight's metalwork.
Indeed, and it sounds as if he has done that - and, IMO, in a not unreasonable way.IMO, its up to the OP to make his own risk assessment and decide how to proceed.
No, that is my point; the classification depends on the design and what is required.What I mean is that IF a device has exposed-c-ps and IF it is not Class II or III then it is Class I IF those exposed-c-ps are (as required) earthed.
There may be no difference in the construction of the housing of 0, I, II, or III items; the difference is in the construction of the electrical parts and hence the requirements.My understanding is that there is not necessarily any difference (of design/construction) between a Class 0 and Class I device, the distinction really depending upon whether or not the exposed-c-ps are earthed.
I suppose that is true because Class 0 is just Class I without the earth (I think).In other words, if one took a (probably 'not permitted') "Class 0" appliance and earthed it's exposed-c-ps, would it not become Class I (and 'permitted')?
What do you mean by 'outside' of the double insulation?It's obviously true that a Class II appliance is Class II because of the double insulation (or equivalent). I'm not so sure about "should not be earthed". If there are extraneous-c-ps ('outside' of the double insulation), I don't think there is any prohibition from earthing them (not that there would be any point), is there?Similarly, a Class II appliance is so because it is double insulated and should not be earthed - not because it is not earthed.
I am not sure if a regulation would have been violated as they do not normally state 'don't do something which is not necessary'.Again, yes, that's obviously why it's Class III, but my comment/question about "should not be earthed" again apply. Are you suggesting that if, whilst it was still SELV, some regulations would have been violated had the exposed-c-ps been earthed?Also, a Class III appliance is so because it is SELV and should not be earthed - not because it is not earthed.
I was talking about all aspectsof construction, including that of the 'electrical parts'.No, that is my point; the classification depends on the design and what is required.What I mean is that IF a device has exposed-c-ps and IF it is not Class II or III then it is Class I IF those exposed-c-ps are (as required) earthed.There may be no difference in the construction of the housing of 0, I, II, or III items; the difference is in the construction of the electrical parts and hence the requirements.My understanding is that there is not necessarily any difference (of design/construction) between a Class 0 and Class I device, the distinction really depending upon whether or not the exposed-c-ps are earthed.
Exactly. If I'm not mistaken, you have talked yourself around to agreeing with my very point [and, conversely, Class I is just Class 0 with earthing connected to the exposed parts - Class 0I {or is it oI?} sort-of recognises that].I suppose that is true because Class 0 is just Class I without the earth (I think).In other words, if one took a (probably 'not permitted') "Class 0" appliance and earthed it's exposed-c-ps, would it not become Class I (and 'permitted')?
I don't totally follow - do you mean 'for safety reasons' or 'because of the MIs'? - which aren't necessarily the same thing! Apart from the fact that it is theoretically undesirable to 'unnecessarily earth' anything (be it a metal Class II appliance, a bath, doorknob or spoon!), are you aware of any specific safety issues associated with earthing exposed metal parts of a Class II device/appliance?There are metal Class II fittings which must not be earthed for safety reasons but if for no other reason than the MIs.
See above.I am not sure if a regulation would have been violated as they do not normally state 'don't do something which is not necessary'. However, earthing isolated parts is not a good idea.