My CH and water comes on at 6.30 in the morning and again at 16.30. All the radiators are hot in the morning but in the evening, those downstairs are tepid. Upstairs are still hot at night. Any ideas? This has only recently happened.
Because in the evening the CH is competing with the HW for the available flow of hot water and the downstairs rads have longer pipe runs and suffer the most. In the morning the HW is up to temperature and doesn't compete. Solution is to fit valve on HW circuit to restrict flow thus allowing more flow to CH side.