I'm on my 4th Drayton mid position MA1 valve in two years and wonder if my problems have been discussed before, with any results or suggestions greatly appreciated.....
The pottery on programmer will allow the valve to operate in the normal way, i.e. hot water only, heating only, or mid -position with both services activated.
(I'll add at this point to say I have changed the brass valve body each time the Drayton has failed, although it was finding - turning free each time.)
The issue I have is that the failures occur after the Heating regularly comes on at say, 05.00 hrs each morning until 09.00 hrs.
During this time the Hot water comes on at 06.00hrs and is set to go off at say 07.30hrs., however, as the Hot water switches off at 07.30hrs as planned it switches the complete system off ( I e. The supply to the boiler and the Heating fails to run on until it's switch-off time of 09.00 hrs
Each time it occurs I find by giving the 3port actuator head a jolt with the palm of my hand, there is a "click" ( as if a micro switch is released) from being stuck and is activated into switching the pumps back on and presumably the boiler supply re-activated and the system then fires back into service until the correct switch off time of 09.00 hrs.
This has happed with unbelievable consistency to all 4 no. New replacement valves and actuators! ( And I'm more than fed-up with replacing the valves and actuators.
Couple of my considerations:
A) the hot water cylinder thermostat is broken? - but this seems to work ok and is not instrumental in switching the hot water service off - the hot water is switched off by the programmer, so I've discounted replacing that.
B) The micro switches in the actuator are stiff? - but the actuators are all brand new , so shouldn't be a problem.?
Valve set-up
C) The Hot water never reaches the thermostat set temperature, so the stat. is still actually calling for heat, when the programmer switches the Hot water off side of the program off.
At which point the system should switch to Heating, ( that always fails!).
Should I just swap to Honeywell or a cheap Chinese eBay £25 set up?
Any suggestions gratefully received.
Cheers, Art.
The pottery on programmer will allow the valve to operate in the normal way, i.e. hot water only, heating only, or mid -position with both services activated.
(I'll add at this point to say I have changed the brass valve body each time the Drayton has failed, although it was finding - turning free each time.)
The issue I have is that the failures occur after the Heating regularly comes on at say, 05.00 hrs each morning until 09.00 hrs.
During this time the Hot water comes on at 06.00hrs and is set to go off at say 07.30hrs., however, as the Hot water switches off at 07.30hrs as planned it switches the complete system off ( I e. The supply to the boiler and the Heating fails to run on until it's switch-off time of 09.00 hrs
Each time it occurs I find by giving the 3port actuator head a jolt with the palm of my hand, there is a "click" ( as if a micro switch is released) from being stuck and is activated into switching the pumps back on and presumably the boiler supply re-activated and the system then fires back into service until the correct switch off time of 09.00 hrs.
This has happed with unbelievable consistency to all 4 no. New replacement valves and actuators! ( And I'm more than fed-up with replacing the valves and actuators.
Couple of my considerations:
A) the hot water cylinder thermostat is broken? - but this seems to work ok and is not instrumental in switching the hot water service off - the hot water is switched off by the programmer, so I've discounted replacing that.
B) The micro switches in the actuator are stiff? - but the actuators are all brand new , so shouldn't be a problem.?
Valve set-up
C) The Hot water never reaches the thermostat set temperature, so the stat. is still actually calling for heat, when the programmer switches the Hot water off side of the program off.
At which point the system should switch to Heating, ( that always fails!).
Should I just swap to Honeywell or a cheap Chinese eBay £25 set up?
Any suggestions gratefully received.