Correct, but as the heating is gas fired and the heat transfer medium is water it shows that the internal water system is in all probability in contact with the general mass of earth. So all the bonding needs to be in place
True, but I don't think for the reason being discussed - I suspect that is there to cater for situations in which 'centralised' central heating (e.g. in a block of flats) resulted in pipes entering the premises as e-c-ps.Central heating is one of the items listed as possible extraneous-conductive-parts in 411.3.1.2 and as such shall be main-bonded.on the ground floor all the heating pipework is within the concrete floor screed, I would class that as being in contact with the general mass of earth!
I don't doubt it - that's the same as my concerns about exported TN-C-S earths to outbuildings with potentially conductive floors in contact with the underling 'earth'. [of course, if I wanted to start a riot, I might point out that, even with a lost supply neutral, they wouldn't get a shock from taps whilst standing on a conductive concrete floor if there were no bonding of the pipework ]The reality of the beast is that it not unknown that in cases of lost neutral faults, it is not unknown for us to receive reports of shocks from taps etc in kitchens with concrete floors!
I don't understand the reason to say that.Correct, but as the heating is gas fired
Then it will likely be connected via the tank/boiler etc. to the CH main bonding if correctly installed.and the heat transfer medium is water it shows that the internal water system is in all probability in contact with the general mass of earth. So all the bonding needs to be in place
They can if they are isolated.What I am trying to do is show that in a lot of cases the separate services cannot be looked at in isolation.
I presume you mean THE earth.So if it appears that the water is by, say, inspection not in contact with earth it probably will be by being connected to other services
It's presumably likely to become an increasing debate - 'over half a century ago', there were probably no non-metalic service supply pipes; in another half a century or so, there may be few metal ones left.I think the chances of being able to guarantee that a metallic piping system throughout an entire house is sufficiently isolated from stray earth paths as to be better left unbonded are slim, to put it mildly. When that fact was recognized and the need for bonding understood (and written into the Wiring Regs.) well over half a century ago, I find it rather curious that it can still attract this sort of debate today.
I agree that it doesn't specifically mean 'services entering a building', but nor does it mean "any metalic parts.....". Rather, it means 'any metallic parts inside the building which are not part of the electrical installation and which are 'liable to introduce a potential (generally earth potential'. In practice, that essentially boils down to metallic parts (mainly pipework) in electrical continuity with 'services entering the building' - otherwise it's very hard to see how it can 'introduce a potential'.Its a common misconception that extraneous refers to services entering a building, it does not, it means any metallic parts inside the building that are not part of the electrical installation.
That's where people start disagreeing. If the meter were removed there would theoretically be no need for bonding of the house-side pipework.Also despite what the regs say, main bonding should always bridge any meter conected to metal pipes, so that if the meter is removed the pipes remain bonded.
I've often seen that said, but I've certainly seen a number of premises in which it is not the case.Plastic gas supplies change to steel before entering buildings.
Why do you/anyone think they do not? Just interested, not disagreeing.Also despite what the regs say, main bonding should always bridge any meter conected to metal pipes, so that if the meter is removed the pipes remain bonded.
I presume the point is that I think one would be hard pressed to find anything in the regs which actually says that. The attitude of the regs seems to be that so long as any conductor 'liable to introduce a potential' is bonded close to where it enters a property, then that's all that matters.Why do you/anyone think they do not? Just interested, not disagreeing.Also despite what the regs say, main bonding should always bridge any meter conected to metal pipes, so that if the meter is removed the pipes remain bonded.