if your earth loop is too high for the device, how can you fix the problem ?
upgrade Earth conductor CSA
upgrade live conductor CSA
or, change the device for one which trips easier
any other ways ?
We got a problem after a test was carried out on a school...
A fuseboard is supplied from the main intake in a school, supplied in MI cable, the impedance was measured at 0.41ohms which was too high for the fuse protecting it to break quick enough
-As it was MI we checked the lock rings etc, which were loose, tried it again and no change in value
-Tried putting a banjo on, no change
-Tried running an additional 10mm earth - no change
the Ze is ok, and so is the EFLI at other boards around the school, just not this one
Any ideas ?
upgrade Earth conductor CSA
upgrade live conductor CSA
or, change the device for one which trips easier
any other ways ?