AAUI, the concern here is to have no significant PD between the car and the surface on which it is standing (and insulated from by its tyres). Any significant PD between the car and its surroundings could prove "interesting" for someone who provides a path between the two, for example when they go to open the car door.
As we know, the potential of a TN-C-S CPC can be significantly above that of the surrounding ground, and it is for this reason that the use of a local earth rod connected to the charging point, and isolation from the TN-C-S CPC is needed. The earth rod should really be close to the area on which the vehicle is standing, to minimise PD between the vehicle and the surrounding ground.
I believe the "diagnostic box" contains a DC sensitive RCD. The wall mounted Polar charger I have for my Ampera does, so I don't need an expensive DC sensitive RCD in the CU.
I note that 17th ( 722.411.4.1) specifically states that the regulation "need not be applied for the charging point at a dwelling if none of (i), (ii) or (iii) is reasonably practical"
As we know, the potential of a TN-C-S CPC can be significantly above that of the surrounding ground, and it is for this reason that the use of a local earth rod connected to the charging point, and isolation from the TN-C-S CPC is needed. The earth rod should really be close to the area on which the vehicle is standing, to minimise PD between the vehicle and the surrounding ground.
I believe the "diagnostic box" contains a DC sensitive RCD. The wall mounted Polar charger I have for my Ampera does, so I don't need an expensive DC sensitive RCD in the CU.
I note that 17th ( 722.411.4.1) specifically states that the regulation "need not be applied for the charging point at a dwelling if none of (i), (ii) or (iii) is reasonably practical"