Earthing bath

Joined
27 Dec 2006
Messages
660
Reaction score
10
Location
London
Country
United Kingdom
and another question if anyone can help . .

I recently fitted a new steel bath to replace an ancient cast iron one. the old bath appeared earthed so I dutifully connected the cable to the new bath . . then over christmas I was replacing some floorboards and discovered a loose earth wire not connected to anything. further investigation revealed the other end of it was my bath earth - so the old bath was in fact not earthed at all.

the flat is in a block with shared cast iron wastes going to the ground -
will connecting the earth wire to the caste iron wate provide a suitable earth?

thanks!
 
Sponsored Links
thanks JohnD - so I have to extend this earth cable down to the main earth point in CU? or gas mains pipe?
 
Sponsored Links
No. You were talking about Supplementary Bonding of the bathroom. This requires the CPC of each electrical circuit that enters the bathroom to be connected to each metallic pipe that enters the bathroom with 4mm G&Y.

The Gaspipe to the CU is Main Bonding which also needs to have been done, but is different. It requires the Main Earth of the installation to be connected to each metallic Service entering the house from outside (water, gas, oil, air conditioning ducts) with 10mm G&Y
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top