Sizing Earthing conductor
This is the cable from the supply cable (SWA) to the MET ( an earth block)
Clamp is a Bs 951 earth clamp - not acceptable on lead, is that still the case on SWA?
Cable looks to be 4mm2 but could be 6mm2
Now I understand that this is nothing to do with me and I should not touch it.
Length of cable 20cm being its a clamp its easy enough to change. Would you?
I am presuming clamping onto SWA is safer than clamping onto lead?
How would the DNO terminate the EC.
Is the cable big enough though
1361 fuse 60 A
TNS
Ze 0.10
Disconnection time 0.1
230/ .10=2,379
2379x2379 = 5,659,641 x 0.1 = 565,961 sqroot =752 /115 = 6.5 mm2
Is that correct.
The low Ze would suggest a good earth Correct?
but this good earths low Ze gives a high fault current
which gives a lower disconnection time, which will push up the size of the cable needed?
Eh!
I've confused myself
This is the cable from the supply cable (SWA) to the MET ( an earth block)
Clamp is a Bs 951 earth clamp - not acceptable on lead, is that still the case on SWA?
Cable looks to be 4mm2 but could be 6mm2
Now I understand that this is nothing to do with me and I should not touch it.
Length of cable 20cm being its a clamp its easy enough to change. Would you?
I am presuming clamping onto SWA is safer than clamping onto lead?
How would the DNO terminate the EC.
Is the cable big enough though
1361 fuse 60 A
TNS
Ze 0.10
Disconnection time 0.1
230/ .10=2,379
2379x2379 = 5,659,641 x 0.1 = 565,961 sqroot =752 /115 = 6.5 mm2
Is that correct.
The low Ze would suggest a good earth Correct?
but this good earths low Ze gives a high fault current
which gives a lower disconnection time, which will push up the size of the cable needed?
Eh!
I've confused myself